VicS
Well-known member
VicS: Yes agree, but Boathook made no mention of a double pole RCD. Shore power is likely to have its own RCD, but unless the trip current discrimination is adequate (or time delayed), no guarantee which one trips first.
RCBO normally takes up just one width slot in the consumer unit (although one width slot RCBO’s may by now be available, I've not checked recently). So it’s a degree of extra protection if space in the consumer unit is limited. And of course makes nuisance tripping of RCD’s serving multiply circuits easier to trace if using RSBO’s instead, with one per each circuit.Thanks for your ISO document links, I’d not seen them, must read through them over Christmas.
It doesnt matter if the RCBO does trip first. A 2 pole upstream RCD will still offer protection against electrocution arising from contact with the boats neutral wiring when the polarity is reversed.
I've done a bit of reading on RCBOs and the 17th edition of the IEE regs since making my earlier post so beginning to understand the logic a bit better now.
The thing is the IEE regs apply to buildings. There may be some special considerations regarding boats, but we tend to use or adapt the installation components that are produced to comply with the IEE regs.
2 pole RCBOs exist but as far as I can see are 2 bays wide so costly on space. The 17th edition regs only require single pole RCBOs as far as I can see.
It will be interesting to see what changes there are in the next edition of ISO 13297. I believe it has been compiled and submitted for approval. It will take into account some of the current American practices required by ABYC standards etc I would think.
Some explanations of consumer unit wiring in connection with the 17 edition regs HERE Should anyone be interested.