Help! Shore Power Problem

Petronella

Member
Joined
29 May 2004
Messages
316
Location
Scarborough Marina, Australia
Visit site
Hi

Shore power to Mehalah in Panama was working fine. Shore power now we are in Australia is no longer working. We can't work out what is wrong

Here is the setup:

- Shorepower lead from pedestal to boat.
- Cable from boat to three way switch (Off/Generator/Shorepower).
- Cable from threeway switch to consumer box with GFI and two circuit breakers, one to water heater (A), the second to every other 240 appliance (B).

This is what happens:

As soon as the GFI breaker is set to On the pedestal breaker trips. This happens even if the two circuit breakers (A and B) are switched off! And even if one or both are physically disconnected. The only time the pedestal breaker does not trip is if the entire consumer unit is physically disconnected!

What we have tried:

- Replacement Shorepower lead
- Bypassing the threeway switch
- Bypassing the GFI
- Every combination of breaker/GFI settings we can think of.

The result is always the same. GFI On, pedestal breaker trips.

What is going on? Thanks for your help. This is my last chance before forking out for a proper marine electrician.
 

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
15,884
Location
Suffolk
Visit site
Hi

Shore power to Mehalah in Panama was working fine. Shore power now we are in Australia is no longer working. We can't work out what is wrong

Here is the setup:

- Shorepower lead from pedestal to boat.
- Cable from boat to three way switch (Off/Generator/Shorepower).
- Cable from threeway switch to consumer box with GFI and two circuit breakers, one to water heater (A), the second to every other 240 appliance (B).

This is what happens:

As soon as the GFI breaker is set to On the pedestal breaker trips. This happens even if the two circuit breakers (A and B) are switched off! And even if one or both are physically disconnected. The only time the pedestal breaker does not trip is if the entire consumer unit is physically disconnected!

What we have tried:

- Replacement Shorepower lead
- Bypassing the threeway switch
- Bypassing the GFI
- Every combination of breaker/GFI settings we can think of.

The result is always the same. GFI On, pedestal breaker trips.

What is going on? Thanks for your help. This is my last chance before forking out for a proper marine electrician.
If the breakers in the consumer unit are single pole, open the consumer unit and disconnect the neutral to the water heater.
 

VicS

Well-known member
Joined
13 Jul 2002
Messages
48,237
Visit site
You could inadvertently have a neutral to earth connection,,,,,,,,like the bonding on an inverter? Is your 3 way switch double pole?

Is the supply center tap to earth?
Agreed........... A neutral to earth fault .............Water heater element a likely culprit, hence PR 's suggestion, together with the on board GFI being less sensitive, or slower to trip , than the pedestal GFI, or even faulty !

Cannot explain why there was no problem in Panama though.
 

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
15,884
Location
Suffolk
Visit site

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
15,884
Location
Suffolk
Visit site
Agreed........... A neutral to earth fault .............Water heater element a likely culprit, hence PR 's suggestion, together with the on board GFI being less sensitive, or slower to trip , than the pedestal GFI, or even faulty !
Not sure why, but almost every time an RCD trip, or a short onboard causes an RCBO to trip, it trips on the pontoon.
Cannot explain why there was no problem in Panama though.
Sods law, just to confound one.
 

Graham376

Well-known member
Joined
15 Apr 2018
Messages
7,528
Location
Boat on Mooring off Faro, Home near Abergele
Visit site
You could inadvertently have a neutral to earth connection,,,,,,,,like the bonding on an inverter? Is your 3 way switch double pole?

Is the supply center tap to earth?

Yes, that happened to us after having installed a new inverter which appeared to have earth and neutral bonded. Unplugged from the inverter and shore power worked OK.
 

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
15,884
Location
Suffolk
Visit site
Yes, that happened to us after having installed a new inverter which appeared to have earth and neutral bonded. Unplugged from the inverter and shore power worked OK.
Something wrong with that installation Graham, or the inverter. Fixed installation inverters should have Earth and neutral bonded at source, but that shouldn't trip shore power, as when on shore power the inverter should be isolated by a double pole changeover switch. Perhaps your switch was only single pole ?
 

Graham376

Well-known member
Joined
15 Apr 2018
Messages
7,528
Location
Boat on Mooring off Faro, Home near Abergele
Visit site
Something wrong with that installation Graham, or the inverter. Fixed installation inverters should have Earth and neutral bonded at source, but that shouldn't trip shore power, as when on shore power the inverter should be isolated by a double pole changeover switch. Perhaps your switch was only single pole ?

No changeover switch fitted at the time, it was a very recent part installation. Double pole switch fitted afterwards.
 

jdc

Well-known member
Joined
1 Dec 2007
Messages
1,963
Location
Falmouth
Visit site
...

Shore power, centre tapped ?
This is not an attempt to answer the OP's query, but just a by-the-way. But I have seen something equivalent to centre tapped mains. In Brazil they have 127V three-phase, which is served up on marinas as single phase to yachts expecting 110V and between two phases (so 220) for those wanting 230V.

Rather different to UK practice, and it puzzled me greatly as my boat's earth polarity fault neon always lit (even when I'd swapped L & N in the 16A plug - which I'd had to do several times in the Canaries and Cape Verde).
 

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
15,884
Location
Suffolk
Visit site
This is not an attempt to answer the OP's query, but just a by-the-way. But I have seen something equivalent to centre tapped mains. In Brazil they have 127V three-phase, which is served up on marinas as single phase to yachts expecting 110V and between two phases (so 220) for those wanting 230V.

Rather different to UK practice, and it puzzled me greatly as my boat's earth polarity fault neon always lit (even when I'd swapped L & N in the 16A plug - which I'd had to do several times in the Canaries and Cape Verde).
It was like that on some pedestals, in Manoel Island, Malta around 2001. Caused no end of fun.
Interesting, never come across it, thanks for sharing (y)
 
Last edited:

VicS

Well-known member
Joined
13 Jul 2002
Messages
48,237
Visit site
Thoughts spring to mind of ENR ......
Dont see it if the GFI is tripping with both circuit breakers open. Would need some load wouldn't it unless there was also a neutral to earth fault.

Perhaps you could explain.
 

William_H

Well-known member
Joined
28 Jul 2003
Messages
13,681
Location
West Australia
Visit site
As far as I know 240v power systems in Oz and earthing /neutral are similar to UK system. Probably vastly different to US and like countries.
I woulds suggest try with water heater disconnected. Typical failure mode for imersion element is corrosion through outer coating causing short circuit of element to ground. of course if it is a 120v element that would cause over current. ol'will
 

Refueler

Well-known member
Joined
13 Sep 2008
Messages
17,814
Location
Far away from hooray henrys
Visit site
Dont see it if the GFI is tripping with both circuit breakers open. Would need some load wouldn't it unless there was also a neutral to earth fault.

Perhaps you could explain.


Wasn't meant as a possible for this guys problem ... it was all the talk about earth etc - just reminded me of discussions over here about how to ground my house - as it needed rewiring from the old Soviet system ...
 