Kohler/ Medusa generator voltage change ?

123zak

New member
Joined
1 Jul 2024
Messages
2
Visit site
1000001648.jpgdoes anyone know can this part of a generator be changed? I.e. seapped from 110v to 240v? Thanks
 
Last edited by a moderator:

Stingo

Well-known member
Joined
17 Oct 2001
Messages
14,071
Location
Getting drunk with your daughter
Visit site
Im no expert on these things, but I'm under the impression that there's a gizmo called a governor somewhere in there, which controls the revs. That's all that needs to be changed and it's a simple job for a diesel mechanic.
 

wonkywinch

Well-known member
Joined
30 Jul 2018
Messages
2,036
Location
Hamble, UK
Visit site
The label on it looks like it might have voltage taps on it somewhere. Normally 115v is two windings in parallel, 230v the windings in series.

Screenshot_20240701_145943_Brave.jpg

This is the actual diagram of your generator from the makers website so you'll find the colour coding correct (hopefully) >>

Screenshot_20240701_150622_Adobe Acrobat.jpg

Download area | Alternator Manuals | Mecc Alte

Remove parallel links from 1>3 and 2>4 then link pins 2 & 3 and take your 230v from 1 & 4.
 
Last edited:

Refueler

Well-known member
Joined
13 Sep 2008
Messages
20,461
Location
Far away from hooray henrys
Visit site
Yes they can be ... its to do with windings / tap points

I've had a Genny changed years ago ...

But it may be that costs are not so attractive today ... if I was to look at it again - I would just buy a new genny.
 

The Q

Well-known member
Joined
5 Jan 2022
Messages
1,907
Visit site
Do a search online for the manual, for the generator. Or contact the makers / distributors on the label they'll know .

I note on the label it says V 57/115/230, which suggests there is a way of switching or changing links to choose the voltage you require..
Do a search online for the manual, for the generator.

It also says Amps 2. 09 / 1.04, which suggests it will give 2 amps at 115V or 1 Amp at 230V.

I wonder if the socket is American wired? Live to earth 115V, neutral to earth 115V,( different phase) , live to neutral 230V..
Wouldn't be the first genny I've found like that...



or you can buy a step up transformer as often used on building sites.
Carroll & Meynell 3000VA Intermittent Step-Up Isolation Transformer 110V/230V Blue - Screwfix
 

wonkywinch

Well-known member
Joined
30 Jul 2018
Messages
2,036
Location
Hamble, UK
Visit site
Do a search online for the manual, for the generator. Or contact the makers / distributors on the label they'll know .

I note on the label it says V 57/115/230, which suggests there is a way of switching or changing links to choose the voltage you require..
Do a search online for the manual, for the generator.

It also says Amps 2. 09 / 1.04, which suggests it will give 2 amps at 115V or 1 Amp at 230V.

I wonder if the socket is American wired? Live to earth 115V, neutral to earth 115V,( different phase) , live to neutral 230V..
Wouldn't be the first genny I've found like that...



or you can buy a step up transformer as often used on building sites.
Carroll & Meynell 3000VA Intermittent Step-Up Isolation Transformer 110V/230V Blue - Screwfix
Check again, the current rating is 20.9A (at 115v?) and 10.4A (at 230v?). The power rating box says 2.4kVA which tallies. No need to buy anything, I've provided the link to the manual and relevant page with instructions in my post above.
 

The Q

Well-known member
Joined
5 Jan 2022
Messages
1,907
Visit site
Check again, the current rating is 20.9A (at 115v?) and 10.4A (at 230v?). The power rating box says 2.4kVA which tallies. No need to buy anything, I've provided the link to the manual and relevant page with instructions in my post above.
Yep you're right, as you are with which links to connect / disconnect .
 

123zak

New member
Joined
1 Jul 2024
Messages
2
Visit site
The label on it looks like it might have voltage taps on it somewhere. Normally 115v is two windings in parallel, 230v the windings in series.

View attachment 179334

This is the actual diagram of your generator from the makers website so you'll find the colour coding correct (hopefully) >>

View attachment 179337

Download area | Alternator Manuals | Mecc Alte

Remove parallel links from 1>3 and 2>4 then link pins 2 & 3 and take your 230v from 1 & 4.
Thank you for your help, just need to understand that info?!
I guess there is a cover I need to remove and expose these ''pins/ terminals'' then it might make more sense.
Thanks again.
 