Hi all,
We have a Fischer Panda P6000 6kW generator onboard - 580 hours, annually serviced, always run under load and never knowingly over loaded.
During a recent cruise it became apparent that the generator was audibly struggling under load with engine speed reducing to a point where it sounded as though it was on the verge of conking out (it didn’t, but didn’t sound very healthy so I shut it down). All the time the gen set was running fine and producing approximately 230V at the panel without any load applied. My initial suspect was a defective immersion heater element (2 kW unit), which appeared to be exacerbating our symptoms more than any other high-draw appliance. I have swapped this out (posted about that in June), a surprisingly tedious operation based due to space constraints but our problem remains.
Our water is heating, but not as quickly as it should/had been. We’re still getting around 210V at our sockets so whilst everything is technically working, something feels amiss. I have had a little fiddle with the actuator as the idle speed seemed a bit low, but no real improvement when a significant load is applied - immersion, wife’s hairdryer, coffee machine etc.
Our fuel is clean and the filters are new. Air filter also looks good.
Whilst the generator had been running perfectly until recently, we have had a couple of minor issues this year and I wonder if there could be a connection:
- At last service it was noted that we’d lost a single impeller blade. The unit was not over heating and visibly/audibly producing the intended quantity of raw water at the exhaust so the decision was made to leave for the time being (the heat exchanger is on the bottom of the generator and will require full unit removal to get to – we’re simply not reliant enough to undertake mid-season).
- I had to replace a corroded raw water intake hose which had leaked, causing some connections in the gen set to get wet. This was dealt with very quickly and there are no visible signs of corrosion/damage.
Where should I start please? I’m definitely not a generator aficionado but would like to see if I can resolve myself as engineers are like hens’ teeth at the moment. I am mindful that I’m playing with AC currents here…
We have a Fischer Panda P6000 6kW generator onboard - 580 hours, annually serviced, always run under load and never knowingly over loaded.
During a recent cruise it became apparent that the generator was audibly struggling under load with engine speed reducing to a point where it sounded as though it was on the verge of conking out (it didn’t, but didn’t sound very healthy so I shut it down). All the time the gen set was running fine and producing approximately 230V at the panel without any load applied. My initial suspect was a defective immersion heater element (2 kW unit), which appeared to be exacerbating our symptoms more than any other high-draw appliance. I have swapped this out (posted about that in June), a surprisingly tedious operation based due to space constraints but our problem remains.
Our water is heating, but not as quickly as it should/had been. We’re still getting around 210V at our sockets so whilst everything is technically working, something feels amiss. I have had a little fiddle with the actuator as the idle speed seemed a bit low, but no real improvement when a significant load is applied - immersion, wife’s hairdryer, coffee machine etc.
Our fuel is clean and the filters are new. Air filter also looks good.
Whilst the generator had been running perfectly until recently, we have had a couple of minor issues this year and I wonder if there could be a connection:
- At last service it was noted that we’d lost a single impeller blade. The unit was not over heating and visibly/audibly producing the intended quantity of raw water at the exhaust so the decision was made to leave for the time being (the heat exchanger is on the bottom of the generator and will require full unit removal to get to – we’re simply not reliant enough to undertake mid-season).
- I had to replace a corroded raw water intake hose which had leaked, causing some connections in the gen set to get wet. This was dealt with very quickly and there are no visible signs of corrosion/damage.
Where should I start please? I’m definitely not a generator aficionado but would like to see if I can resolve myself as engineers are like hens’ teeth at the moment. I am mindful that I’m playing with AC currents here…