Help! Shore Power Problem
Petronella
29 May 2004
Scarborough Marina, Australia
Hi
Shore power to Mehalah in Panama was working fine. Shore power now we are in Australia is no longer working. We can't work out what is wrong
Here is the setup:
- Shorepower lead from pedestal to boat.
- Cable from boat to three way switch (Off/Generator/Shorepower).
- Cable from threeway switch to consumer box with GFI and two circuit breakers, one to water heater (A), the second to every other 240 appliance (B).
This is what happens:
As soon as the GFI breaker is set to On the pedestal breaker trips. This happens even if the two circuit breakers (A and B) are switched off! And even if one or both are physically disconnected. The only time the pedestal breaker does not trip is if the entire consumer unit is physically disconnected!
What we have tried:
- Replacement Shorepower lead
- Bypassing the threeway switch
- Bypassing the GFI
- Every combination of breaker/GFI settings we can think of.
The result is always the same. GFI On, pedestal breaker trips.
What is going on? Thanks for your help. This is my last chance before forking out for a proper marine electrician.
PaulRainbow
16 May 2016
Suffolk
Hi
Here is the setup:
What we have tried:
- Bypassing the GFI
If the breakers in the consumer unit are single pole, open the consumer unit and disconnect the neutral to the water heater.
VicS
13 Jul 2002
You could inadvertently have a neutral to earth connection,,,,,,,,like the bonding on an inverter? Is your 3 way switch double pole?
Is the supply center tap to earth?
Agreed........... A neutral to earth fault .............Water heater element a likely culprit, hence PR 's suggestion, together with the on board GFI being less sensitive, or slower to trip , than the pedestal GFI, or even faulty !
Cannot explain why there was no problem in Panama though.
PaulRainbow
16 May 2016
Suffolk
PaulRainbow
16 May 2016
Suffolk
Not sure why, but almost every time an RCD trip, or a short onboard causes an RCBO to trip, it trips on the pontoon.
Sods law, just to confound one.
Graham376
15 Apr 2018
Yes, that happened to us after having installed a new inverter which appeared to have earth and neutral bonded. Unplugged from the inverter and shore power worked OK.
PaulRainbow
16 May 2016
Suffolk
Something wrong with that installation Graham, or the inverter. Fixed installation inverters should have Earth and neutral bonded at source, but that shouldn't trip shore power, as when on shore power the inverter should be isolated by a double pole changeover switch. Perhaps your switch was only single pole ?
Graham376
15 Apr 2018
No changeover switch fitted at the time, it was a very recent part installation. Double pole switch fitted afterwards.
jdc
1 Dec 2007
Falmouth
Shore power, centre tapped ?
This is not an attempt to answer the OP's query, but just a by-the-way. But I have seen something equivalent to centre tapped mains. In Brazil they have 127V three-phase, which is served up on marinas as single phase to yachts expecting 110V and between two phases (so 220) for those wanting 230V.
Rather different to UK practice, and it puzzled me greatly as my boat's earth polarity fault neon always lit (even when I'd swapped L & N in the 16A plug - which I'd had to do several times in the Canaries and Cape Verde).
PaulRainbow
16 May 2016
Suffolk
It was like that on some pedestals, in Manoel Island, Malta around 2001. Caused no end of fun.
Interesting, never come across it, thanks for sharing (y)
VicS
13 Jul 2002
Thoughts spring to mind of ENR ......
Dont see it if the GFI is tripping with both circuit breakers open. Would need some load wouldn't it unless there was also a neutral to earth fault.
Perhaps you could explain.
William_H
28 Jul 2003
West Australia
As far as I know 240v power systems in Oz and earthing /neutral are similar to UK system. Probably vastly different to US and like countries.
I woulds suggest try with water heater disconnected. Typical failure mode for imersion element is corrosion through outer coating causing short circuit of element to ground. of course if it is a 120v element that would cause over current. ol'will
Refueler
13 Sep 2008
Far away from hooray henrys
Wasn't meant as a possible for this guys problem ... it was all the talk about earth etc - just reminded me of discussions over here about how to ground my house - as it needed rewiring from the old Soviet system ...