Grounding generators

Graham_Wright

Well-known member
Joined
30 Dec 2002
Messages
7,736
Location
Gloucestershire
www.mastaclimba.com
Son is part of a crew bringing back a dredger from Spain.

He is concerned to note the absence of a general earthing system.

If the generators (single and 3 phase) are not earthed, would not the volts relative to the hull float?

Perhaps there is an hidden or accidental leak between the outputs and hull.

I have asked him to make some measurements but he is now incommunicado.
 

sailaboutvic

Well-known member
Joined
26 Jan 2004
Messages
9,983
Location
Northern Europe
Visit site
Son is part of a crew bringing back a dredger from Spain.

He is concerned to note the absence of a general earthing system.

If the generators (single and 3 phase) are not earthed, would not the volts relative to the hull float?

Perhaps there is an hidden or accidental leak between the outputs and hull.

I have asked him to make some measurements but he is now incommunicado.

I was advise by FP not to Earth the generator to the boat
 

status

Member
Joined
17 Apr 2008
Messages
573
Location
West Mids.
Visit site
If the genny is not connected to the hull there will be no pd as there is no circuit, there can only be a pd across the conductors of the genny?
 

mjcoon

Well-known member
Joined
18 Jun 2011
Messages
4,453
Location
Berkshire, UK
www.mjcoon.plus.com
If the generators (single and 3 phase) are not earthed, would not the volts relative to the hull float?

My hazy recollection of my electrical machines lectures is that three-phase can be either star (which has an obvious earth point) or delta (which doesn't).

In any case there is another potential earthing point at the consuming devices. Note that in UK domestic installations the earth is part of the safety system and consumers do not earth the neutral line...

Mike.
 

Graham_Wright

Well-known member
Joined
30 Dec 2002
Messages
7,736
Location
Gloucestershire
www.mastaclimba.com
3 phase generators produce 230 v between star and any phase and 420 volts between phases.

Consumer protection nowadays relies on the current out (L) equalling current in (N). Any difference will cause the breaker to trip. If there is a difference, it is due to current out finding a different route back. If the generator output is not earthed it could well balance out and not detect the difference.
 

lw395

Well-known member
Joined
16 May 2007
Messages
41,951
Visit site
Some electrical systems float completely.
It means a fault to earth at any one point is not a problem.
E.g. if you accidentally earth the live, no current flows, you just force the Neutral 230V away from earth. 2 simultaneous faults would be messy though.
 

Graham_Wright

Well-known member
Joined
30 Dec 2002
Messages
7,736
Location
Gloucestershire
www.mastaclimba.com
Some electrical systems float completely.
It means a fault to earth at any one point is not a problem.
E.g. if you accidentally earth the live, no current flows, you just force the Neutral 230V away from earth. 2 simultaneous faults would be messy though.

………if you accidentally earth the live - perhaps through yourself?!
 

rogerthebodger

Well-known member
Joined
3 Nov 2001
Messages
12,483
Visit site
IMHO when you are looking at "grounding " generators there are 2 things you need to consider

1) is the grounding of the frame of the generator. That is to ensure that the frame of the generator does not get to a voltage above the grounding point so the frame is safe to touch.

2) and more important is to detect any current leakage between the line voltage and a potential point that a person can come into contact with.

This diagram gives one method of doing that.

808ecm13fig1.gif


This also gives some more infomation

http://www.ecmweb.com/content/monitor-ground-fault-leakage-currents
 

Graham_Wright

Well-known member
Joined
30 Dec 2002
Messages
7,736
Location
Gloucestershire
www.mastaclimba.com
IMHO when you are looking at "grounding " generators there are 2 things you need to consider

1) is the grounding of the frame of the generator. That is to ensure that the frame of the generator does not get to a voltage above the grounding point so the frame is safe to touch.

2) and more important is to detect any current leakage between the line voltage and a potential point that a person can come into contact with.

This diagram gives one method of doing that.

808ecm13fig1.gif


This also gives some more infomation

http://www.ecmweb.com/content/monitor-ground-fault-leakage-currents

That was what I thought and recommended. Unfortunately, he is out of contact now, en route for the UK (with a 3 foot freeboard!).

I trust he took my advice.
 

lw395

Well-known member
Joined
16 May 2007
Messages
41,951
Visit site
………if you accidentally earth the live - perhaps through yourself?!

Indeed.
I worked for a while in a high voltage lab where very little was earthed.
You could touch live circuits with one hand and all you would feel was a tiny current due to capacitance completing the circuit.
If you touched two different parts of the circuit you were either fried or fired.

The point is, there are several ways to not kill people with electricity.
The one we are used to is having earth bonded and neutral similar to earth.
Other systems can be better, but you have to understand the system and apply it properly.
You cannot randomly mix and match based on a limited understanding.

I'm sure there are lots of regulations that apply to ships, demanding what systems are used, but that is not my field.
 