The rubber pipe in the gas locker from the solenoid cut off to the copper pipe to the cooker & heater had come loose so I refitted the hose clip secure again. I just thought it was normal wear and tear where things can come loose. When I put on the gas valve I could hear gas flowing but there was no leak but I was not happy so switched off the gas valve. I checked the locker and bilges and the pipe run but no smell of gas. So with the gas off I turned on the cooker burner and lit it and there was a real flash flame about a foot long. It would seem that the regulator was not regulating and higher pressure gas was passing into the system and what I heard for 2/3 seconds when it was on was the pressure filling up the pipework.
I had not considered the possibility of a regulator failure in this way and if I had not had a little warning by the pipe being blown off initially I would certainly now be in hospital or mortuary. The regulator was a well known Italian make and 5 years old.
My gas system follows all the recommendations regarding locker set up, pipe joints at bulkheads, bubble leak, isolating solenoid, dated flexible pipes etc but I am now thinking about a pressure gauge in the line and visible from the cooker. This sort of problem is probably very rare but the consequences of lighting a stove with high pressure propane from the burner is a horrific situation that I do not wish to risk and I do not see any alternative to a pressure gauge.
I had not considered the possibility of a regulator failure in this way and if I had not had a little warning by the pipe being blown off initially I would certainly now be in hospital or mortuary. The regulator was a well known Italian make and 5 years old.
My gas system follows all the recommendations regarding locker set up, pipe joints at bulkheads, bubble leak, isolating solenoid, dated flexible pipes etc but I am now thinking about a pressure gauge in the line and visible from the cooker. This sort of problem is probably very rare but the consequences of lighting a stove with high pressure propane from the burner is a horrific situation that I do not wish to risk and I do not see any alternative to a pressure gauge.