Well-Known Member
The impression I got when I watched the first video is that the mega was initially connected between the line and neutral on the supply side of the RCD. This will NOT cause the RCD to trip as there is no residual current flowing through the RCD. The same when the line/neutral was shorted to the "earth" (centre) tap.
It was only later in the video that the output of the RCD/MCB was shorted to earth (centre tap) or line/neutral.
If I am wrong please tell me.
There was a lot of video of totally expected behaviour to sit through, to find the bit where the Testbox connected between load side of RCD, N or L, to 'E' didn't trip the RCD.
I would suggest that the E terminal of the invertor is not a low impedance to anything resembling zero volts, so connecting the test box to it did not draw anything like 30mA from either N or L.
The fact that connecting 'E' to the incoming DC minus created an error condition on the inverter further shows that 'E' is not a centre tap.
I would speculate that the 'E' pin is some kind of protection which shuts down the inverter if it senses either L or N is shorted to it.
I.e. it's a different protection scheme to find the first fault as I alluded to in Post 56.
I'm no expert on inverters, I am not familiar with wiring regs etc in this field, this is fundamental circuit electronics, which is what I do.