Dockhead
Well-Known Member
You could explain why.That's not good.
Mega fuses have standard interrupt capacity of only 2kA. T-class fuses are typically 20kA. A 200-400AH LiFePo4 battery can produce 10kA and more when shorted.
The reason why this is different from lead is because the current produced in a dead short is inversely proportional to the total resistance in the circuit, and LiFePo4 batteries inherently have internal resistance more than an order of magnitude less than lead batteries. 0.2-0.5 milliohms per cell vs. 5-20 milliohms per cell with flooded lead batteries. So you can have an order of magnitude more current in a short circuit, than with a lead battery bank. This REQUIRES an appropriate fuse. You are playing with fire (literally) if you try to use Mega fuses with lithium. It's totally inappropriate.