It depends on the quality/size of the cable. A cable comes with the spec for what you lose per metre.
I had a mains cable to run (at my home) that sort of distance. You could not use a normal cable but had to use a fairly heavy duty cable that cost a lot and was heavy. The calculation is simple - just ask for the voltage drop per metre of cable then using watts = volts time amps you can see what power can be supported at the far end of the cable.

Paul
 

Geoffs

Active member
Joined
15 Jun 2001
Messages
2,332
Location
Wantage,Oxfordshire
Visit site
I expect you have 2.5mm2 cable for the usual 16amp marina supply. Such cable drops about 7.5mV for every ampere that flows for every metre of cable. Your 600 watt heater will draw about 2.5 amps from 240 volt supply.

So for 300 metres, remember - current has to go there and back, so 600 metres, a quick sum gives 11.25 volts drop. This means that the heater output will actually be about 550 watts. 300 metres is quite a long way, if you can’t use a shorter cable, then a heavier one would help. A 30 amp 6mm2 cable would half the losses.

That's all assuming my arithmetic is right!
 

KevL

New member
Joined
1 Oct 2001
Messages
387
Location
Manchester
Visit site
The sums look about right but I didn't get my calculator out.

11 1/4 V drop should be no problem at all, in fact you should get 600W output from them at that, the reason is simple. A few years back the UK had to "Harmonise" it's elec supply voltage with the rest of europe and an "euro average" voltage was chosen at 230V. Now to supply 230V from the national grid would have meant either changing all the sub stations or the generators at the power stations both of which would have been quite costly. So what did they do, they altered the tolerance on supply voltage and you still get 240V out of your sockets. BUT all new equipment is designed to operate at 230V +10% -5% (from memory) so with your volt drop you will be operating your heaters at the design voltage. Lucky old you.