jdc
Well-known member
Following on from the Garage Consumer Unit thread, I've been wondering for some time about the changing electrical loads boats now impose on the mains supply. There are no regs as such, but I'd like to follow good practice nonetheless, essentially complying with IET edition 18.
RCDs / RCCBs come in various types according to the expected loads. The old type AC devices are no longer considered suitable where there is mains-powered LED lighting or induction ovens or other inverter or switching loads. And for my electric car I had to install a type B.
It strikes me that modern battery chargers and immersion heaters will almost inevitably be inverters / switching devices, especially if there are lot of Lithium batteries on board, so would anyone now recommend installing a type F?
Similarly for MCBs, there are classes B, C and D. Class C is easiest to source, but may not be appropriate on a boat: it's the threshold for instantaneous tripping which is the difference between the types:
Type B - trips between 3 and 5 time full load current
Type C - trips between 5 and 10 times full load current
Type D - trips between 10 and 20 times full load current
If I were doing a new install, I think I'd go for a type F RCD, and type B MCBs, but what do others think reasonable? Presumably it depends on the loads.
RCDs / RCCBs come in various types according to the expected loads. The old type AC devices are no longer considered suitable where there is mains-powered LED lighting or induction ovens or other inverter or switching loads. And for my electric car I had to install a type B.
It strikes me that modern battery chargers and immersion heaters will almost inevitably be inverters / switching devices, especially if there are lot of Lithium batteries on board, so would anyone now recommend installing a type F?
Similarly for MCBs, there are classes B, C and D. Class C is easiest to source, but may not be appropriate on a boat: it's the threshold for instantaneous tripping which is the difference between the types:
Type B - trips between 3 and 5 time full load current
Type C - trips between 5 and 10 times full load current
Type D - trips between 10 and 20 times full load current
If I were doing a new install, I think I'd go for a type F RCD, and type B MCBs, but what do others think reasonable? Presumably it depends on the loads.