Well-Known Member
Fuse the batteries individually for their rating. NH00 fuses are good value. If you are using an inverter, a breaker is a good choice for that instead of a fuse. Fuse that for the rating of the inverter. For example, my 3000w inverter can deal with a surge of 9000w. Its a 24v inverter. I can pull about 115A at 3000w. I installed a 150A Blue Sea breaker. It's only tripped once when I accidently loaded the inverter to 3750w. It took 20mins to trip. The inverter also has its own inbuilt trip. That didn't trip.Oh, are they cheap - I hadn’t noticed!
See they’ve got a pretty conservative continuous discharge rate - still more than enough for me - presumably that is their choice, to prioritise longevity over absolute performance. But I guess I still need to size cable and fuse for the max 400A rate?
I have my 105Ah battery fused at 160A. The 280A battery is fused at 225A. The BMS on both batteries are rated to 200A. The only way I can impose a large load is through the inverter. With this being limited to 150A by the breaker, the main fuses are safe from a premature pop.
Since my batteries are parallel wired, I have to consider that I may run on one battery if I had a BMS failure on the other.
The smaller battery needs to be able to deal with 150A. Although in this situation, I might be a little more careful of my inverter loads