Well-Known Member
Vic, This one of these areas where one regulation may seem contradictory to another section 709 of the 18th edition refers to a TN system however it is against the law (ESQCR) to connect a marina supply directly or indirectly to a PME system which effectively means that you have to have a TT system. All a bit academic for here I suspect. I referred to the TT system in marinas and the Earth Loop Impedance figures with respect to the video posted. I thought that it was somewhat misleading in this context. He does post some excellent videos so not knocking him.Pontoon supplies are earthed to a local earth rod /rods or similar?
I thought they should be a TN -S system or is that simply not an available option.
.
I think that, bottom line, if the OP was referring to a UK marina is, they are in breach of regulations if they are not carrying out annual Installation Inspections and not rectifying faults such as "Reversed Polarity"