Alex_Blackwood
Well-Known Member
Quite right Paul. What the 18th ed. says for marinas. Looks like protection to me. Perhaps I should refrain from using an extension with my lawnmower as well. Equally dangerous?Not sure why i would electrocute myself, my suggestion was a proper shore power inlet, with an onboard RCBO
I didn't suggest an extension lead, neither has anyone else in this thread. Besides, it's rubbish that a boat would fail the BSS for having an extension lead onboard.
More nonsense. an extension lead would surely come aboard via the same route as ashore power lead ?
If someone just used an extension lead or they used a proper shore power installation they would plug the cable into the same receptacle on the pontoon, that's what provides protection to the cable, nothing onboard can do so.
16a sockets on the marina have no fuses, but there is an overrated the lead, huh ??? "Normal" UK shore power is 16a max (of course there are 32a, 64a etc available) and ashore power cable should be 2.5mm, which is typically rated at 30a, even 1.5 is 21a. I think you might find it's a legal requirement for shore power installations to be fitted with RCDs and MCBs or RCBOs.
709.531.2 RCDs
Socket-outlets shall be protected individually by an RCD having the characteristics specified in Regulation 415.1.1.
Devices selected shall disconnect all poles, including the neutral.
709.533 Devices for protection against overcurrent
Each socket-outlet shall be protected by an individual overcurrent protective device, in accordance with the
requirements of Chapter 43.