Electrical issue with AC consumer unit

What is the purpose of the earth connection ?
For testing it by providing a path for the 10ma trip current. My EV charger 10ma Schneider RCDO has a test button next to the lever.
 

Attachments

  • rcbo.jpg
    rcbo.jpg
    34.7 KB · Views: 5
RCBO's also often have an earth wire, or at least the type I have for my EV charger does. L in and out, N out , blue wire for the N in and g/y earth. (it's single width version)
The earth is for testing it and there is a small button next to the lever. If there isn't a test button, its probably a dp mcb with Live + switched Neutral.

RCBOs without Earth wires still have a test button.
 
Looking at the diagram I posted it looks like its only connected to the current difference from the line / neutral and driving the disconnect relay.

As Paul says there are coming out without the earth so some one has designed a system that does not require a PE connection

I note its called FE what ever that means.
 
Looking at the diagram I posted it looks like its only connected to the current difference from the line / neutral and driving the disconnect relay.

As Paul says there are coming out without the earth so some one has designed a system that does not require a PE connection

I note its called FE what ever that means.

Functional earth
 