I dunno what to suggest re airco. When the control board demands compressor, are you getting 230v at the compressor motor? I think that's pink and white/red but I'm not sure because I think there is a switching transistor thing there that chops the A/C sine wave to control speed. Not 100% sure but the three wires and the "SCR" on the diag suggest this. You'd still see some RMS ac voltage though if you used an ordinary multimeter, even if not 230, if the compressor has been asked to run
When are you back on berth? Do you want me to get jenny to deliver the dji? Is in my garage ready to rock. You need an ipad ideally, or a phone. Dji Go from the app store. And a usb leadThanks J. I'll get a meter on it when we are back on berth. For now, however, faced with gruelling F1 winds and overnight lows of 22c, we have decided to tough it out at VF tonight![]()
Ooh yes please. We'll definitely be back late Friday afternoon because we are suppering in Vauban. Shall I call her to find a convenient time?When are you back on berth? Do you want me to get jenny to deliver the dji? Is in my garage ready to rock. You need an ipad ideally, or a phone. Dji Go from the app store. And a usb lead
SCR on the compressor refers to the connections Start Common and Run. The start capacitor connects the power from the run terminal and causes a phase shift to make the compressor turn.
If you have power at the compressor it should run.
To have the thing in permanent cooling I would suggest the wire from the controller to the reversing valve 2nd from right should be disconnected, but this won't stop the compressor running. A stuck reversing valve can cause LP trips, and a light tap with a mallet might release it.
I would check to see if you have both HP and LP switches (not shown in the photos) and see if these have small rubber dimples on the side opposite the pressure connection. If so press these and see if the thing starts.
Running in dehum mode simply runs in cooling mode at low fan power, causing a cold cooling coil with low fan speed, so the moisture condenses out, but not much cooling occurs. Extended running might cause the gas to migrate to the condenser, leading to an LP trip if this unit has one. The LP switch might be colour coded blue, HP red.
The wiring diagram and unit look simple enough. It doesn't look like the compressor is speed controlled, but I do need to study th diagram a bit more.
If power has been getting to the compressor and it isn't running will likely kill it, but simple enough to check with a simple multimeter. Disconnect the power, pull off the connections on the CSR terminals. Then measure the resistances
Common Run - Lowest for this size compressor around 1-2 ohms
Common Start - quite a bit higher ~ 5-7 ohms
Run - Start - higher agin and also CR + CS so 6 - 9 ohms
I suspect the power simply isn't getting through to the compressor.
A final check is to see if you have gas inside the unit. This is a really basic check - remove one of the schraeder charge valve caps and briefly depress the valve pin and see if it hisses fairly hard. With the unit off and assuming your ambient temperature is around 25oC it should be about 8 bar with R417A, so you will definitely know if there is a decent as charge. If you have a gauge with schraeder lifter then you can accurately measure the pressure within.
R417A is also sold as Isceon MO59 (Du Pont now Chemours).
If you can undertake these checks then let me know what you find. Fault finding by forum is not easy, so if you PM me I can give you my direct contact details.
You will find a decent explanation of how a single phase compressor works here ...
https://www.dropbox.com/s/qhkkox4xfaoqc5o/ThermaCom Field Compressor Guide.pdf?dl=0
Also a simple check is the overload klixon on top of the compressor just above the terminals in the diagram. Check for continuity (0 ohms) across the two wires. If these do operate sometimes a rap with a screw driver handle will reset the bimetal strip inside the thing.
Found the HP switch - sorry about poor photo quality, it's a bit inaccessible:
![]()
It's the green thing in centre of pic, yellow wires, red dot in middle.
Would not have thought so ,it would hum and buzz a bit and maybe warm up , plus comp will have been running when in dehumid mode -so unlikely ceased .
If its cutting out something is telling it .
Have you tapped reversing valve few times ,simultaneously starting it @ cold or heat .
If its jammed twixt two maybe comp is told to stop .needs to be fully one way or t,other to allow comp to start
That's what you are seeing I suspect
Your screen will tell you stuff like Lp low pressure etc so it's gotta be something that's NOT displayed normally -assuming the diagnostic function still works .
It's unlikely to be a raw water pump issue -comp starting -nope
Comp should work without water pump initially for a few mins ,then pump raw water turns on to start cooling the refrigerant . After it detects its ready to needcooling .Not necessarily both comp + pump come on together
Also put your hand on the raw water pump should vibrate when it comes on .
You'd get "hpa" error code on the cabin display panel if there was no raw water flow. Sounds like your pump is running ok - ref your close-the-seacock trick
If comp were seized I don't see why the volts across it would fall as you describe
Control board failure? (does happen)