ShinyShoe
Well-known member
Their sealing and flooding systems are pretty sophisticated.I've got to admit that for gas fires unless the CO2 can isolate the fuel from the ignition source OR the oxygen supply it will be ineffective, but as our boats are normally pretty well enclosed spaces which are only open at the top, it would still be my first choice for any inboard fire simply because it is so much cleaner and won't cause much, or indeed any other damage.
I'm a Marine Engineer, and all of the Engine Rooms I have worked in are fitted with CO2 or similar flooding systems, designed to fill the space and exclude the air.
They also do a load of maths to know how much CO2 a sealed compartment needs to extinguish it.
You are looking at something like 30-70% CO2 to extinguish a fire. >5% is harmful to human health so you need to be able to deploy that in a way that you aren't breathing it.
Not sure on the volume of a typical cabin but lets call it 3m long, 1.75m high and 2.25m wide. So you have about 12cu.m.
You can't properly seal it because you have bilges spaces etc not designed to be completely sealed.
At 50% CO2, in 12m - if I understand correctly you would need about 12kg of CO2. A typical CO2 extinguisher in your home might be 2kg, a big workplace one 6kg.
All achievable in an engine compartment where you can have an extinguishing hole and otherwise a pretty sealed space. Where the risk of fire is high. Where the damage from the extinguisher may be more than the fire. Where you are outside on deck tacking it. For the cockpit? Where you can't even deploy the extinguisher till all heads are accounted for, where ever hatch and seal needs to be closed and a shed load of cylinder volume is needed... mmmm?
In the workplace you might well struggle to get approval to even a 2kg CO2 for use in the cabin... ...because you'll risk it being used directly.
On a steel ship this is quite effective. On a plastic boat - designed to be ventilated and make sure people sleeping don't suffocate, filled with lots of lovely soft furnishings and other combustibles. We've seen how things that we expect to be fire resistant (aka cladding on high rise buildings) once a fire is going are far from.One thing I haven't seen mentioned is the value of closing doors, windows, other entrances, and vents which can also smother a fire
My work is very clear - extinguishers are provided because the law says they have to be. They don't expect me to use one. They expect me to get out and get others out. Anything bigger than a standard household kitchen bin size of fire - is considered too big for a standard extinguisher...
Fireblanket for the galley?