For the same safety reasons as applies to the 3 wire polarised system in your house's AC supply (assuming you are in the UK or similar) where AC sources have their neutral bonded to ground (as at the house switchboard) so that the house wiring's earth conductor then provides a return path in the case of fault on an appliance or cabling.
For on a boat most (all?) codes require, to achieve the same thing, that all AC sources have their neutral grounded at the source. So, for example, an installed generator, which is an AC source in the same way as a house's switchboard is an AC source, has its neutral bonded to earth at the generator and same for an invertor.
If the boat has an isolating transformer then the shore neutral (and its earthing) is, of course, isolated from the boat side of the transformer so it cannot be "seen" from the boat's point of view, so the transformer is regarded as an AC source in the same way as an invertor or generator is and the neutral on the output side earthed to again give a 3 wire polarized system on board.
For a portable generator with floating neutral the effect is similar to not correctly bonding to earth an on board transformer's neutral. However, as explained before, if it is plugged into the boat's shorepower connection, as they usually are, then the whole of the boat's AC distribution will be floating neutral (as for other safety reasons the neutral on the boat is lifted from the boat's earth when the AC supply is switched to the shore power connection).
Now one could possibly provide a special switched connection for a portable generator seperate from the shore power one such that the generator's neutral is earthed but I suspect no one does or is likely to do that. Furthermore, while the generators have fault protection built in, I suspect that this will in most (all?) cases enable preventing generation if the neutral is earthed and the generator chassis is also earthed, as it should be, or leaks to earth if it is not (I have not and never will have a need to see if this is so).
From time to time I hear some say that if there is an isolating transformer (or small floating neutral generator) you don't need to earth the neutral on the output side, just as when they are used on land. However, in the land case they are thinking of only a single appliance being normally connected to an isolating transformer, so no other AC distribution/appliances are able to be implicated in a fault situation to cause a shock hazard.
Obviously, people get away with ignoring all of these things, just as in a house incorrect wiring may last the life of the house without the circumstances arising where an accident occurs.
Hope that is clear.
John
For on a boat most (all?) codes require, to achieve the same thing, that all AC sources have their neutral grounded at the source. So, for example, an installed generator, which is an AC source in the same way as a house's switchboard is an AC source, has its neutral bonded to earth at the generator and same for an invertor.
If the boat has an isolating transformer then the shore neutral (and its earthing) is, of course, isolated from the boat side of the transformer so it cannot be "seen" from the boat's point of view, so the transformer is regarded as an AC source in the same way as an invertor or generator is and the neutral on the output side earthed to again give a 3 wire polarized system on board.
For a portable generator with floating neutral the effect is similar to not correctly bonding to earth an on board transformer's neutral. However, as explained before, if it is plugged into the boat's shorepower connection, as they usually are, then the whole of the boat's AC distribution will be floating neutral (as for other safety reasons the neutral on the boat is lifted from the boat's earth when the AC supply is switched to the shore power connection).
Now one could possibly provide a special switched connection for a portable generator seperate from the shore power one such that the generator's neutral is earthed but I suspect no one does or is likely to do that. Furthermore, while the generators have fault protection built in, I suspect that this will in most (all?) cases enable preventing generation if the neutral is earthed and the generator chassis is also earthed, as it should be, or leaks to earth if it is not (I have not and never will have a need to see if this is so).
From time to time I hear some say that if there is an isolating transformer (or small floating neutral generator) you don't need to earth the neutral on the output side, just as when they are used on land. However, in the land case they are thinking of only a single appliance being normally connected to an isolating transformer, so no other AC distribution/appliances are able to be implicated in a fault situation to cause a shock hazard.
Obviously, people get away with ignoring all of these things, just as in a house incorrect wiring may last the life of the house without the circumstances arising where an accident occurs.
Hope that is clear.
John