[ QUOTE ]
... the battery bank is 500ah @ 24v
[/ QUOTE ]Which is, of course, twice the energy capacity of a 12V 500Ah battery bank - i.e. the equivalent of a 12V 1000Ah battery bank[ QUOTE ]
6 kva genny 220volt
[/ QUOTE ]That sounds reasonable for the sort of loads you have[ QUOTE ]
We run the genny when we anchor to cook the evening meal for 1 hour charge the batteries at the same time with chargers totaling 100 amps.
[/ QUOTE ]So you are only replacing around 90Ah per day from the genny - the rest must be coming from solar and running the main engines when you move?[ QUOTE ]
... we increased the charger from 50 a to 100 amps this has cured the problem.
[/ QUOTE ]Do you have the means to monitor the net current flow into the batteries? If so, how long does it take, when the batteries are really low, for the current to fall from around 100A to the C/10 rate - i.e. 50A? I'm just about to order my new batteries - Varta flooded lead acid, 3 x 180Ahr 12V, stated to be Deep Cycle. The old batteries are Sonnenschein gels, around 3 years old and completely shot - I think the previous owner had the battery charger set incorrectly and the gels just couldn't take the continual overcharging. From your experience what do you think of my choice of flooded lead acids?[ QUOTE ]
But if I had to do it again I would probably fit a dc generator about 200 amps double the battery bank and fit 2 invertors about 4 kw total.
[/ QUOTE ]Can you talk me through your reasons - I don't mean to appear to be critical, just interested in hearing what you feel would be better by having a dc genny rather than ac
David
... the battery bank is 500ah @ 24v
[/ QUOTE ]Which is, of course, twice the energy capacity of a 12V 500Ah battery bank - i.e. the equivalent of a 12V 1000Ah battery bank[ QUOTE ]
6 kva genny 220volt
[/ QUOTE ]That sounds reasonable for the sort of loads you have[ QUOTE ]
We run the genny when we anchor to cook the evening meal for 1 hour charge the batteries at the same time with chargers totaling 100 amps.
[/ QUOTE ]So you are only replacing around 90Ah per day from the genny - the rest must be coming from solar and running the main engines when you move?[ QUOTE ]
... we increased the charger from 50 a to 100 amps this has cured the problem.
[/ QUOTE ]Do you have the means to monitor the net current flow into the batteries? If so, how long does it take, when the batteries are really low, for the current to fall from around 100A to the C/10 rate - i.e. 50A? I'm just about to order my new batteries - Varta flooded lead acid, 3 x 180Ahr 12V, stated to be Deep Cycle. The old batteries are Sonnenschein gels, around 3 years old and completely shot - I think the previous owner had the battery charger set incorrectly and the gels just couldn't take the continual overcharging. From your experience what do you think of my choice of flooded lead acids?[ QUOTE ]
But if I had to do it again I would probably fit a dc generator about 200 amps double the battery bank and fit 2 invertors about 4 kw total.
[/ QUOTE ]Can you talk me through your reasons - I don't mean to appear to be critical, just interested in hearing what you feel would be better by having a dc genny rather than ac
David