Shore power wiring
Far to kind ;)
As it happens I know exactly what I'm doing inside a 240v box and a 12v DC box.
My reference to the presumably positive was to the RED CABLE as this would normally be positive. I haven't done a full trace back yet, but at first glance it appears that this is the positive cable connected to a N terminal, though it's difficult to see until I can get to the top of the RCD to look.
The black 2 core is to a polarity indicator light. That comes off the input side of the RCD, so you can check polarity before switching on.
The output cables seem to follow the red / black connections logically, so it would indicate red is indeed positive, but some ( insert appropriate word ) has done a rather poor job of wiring this up.
I will be investigating further, belling out the connections to the shore power inlet to make sure the colours are correct, and then rewiring this monstrosity properly.
I was trying to stop someone killing themselves. Sometimes being blunt is the best way to help, and I was the only one advising from what I had read that the OP did not understand what he was about.
The OP response here still does not give me any confidence at all he does understand AC power.
How does a polarity indicator work on an AC supply ? (although I accept there is a widely mis understood concept of 'Polarity' as far as AC is concerned meaning: is the shore power supply live conductor at the boat end actually connected to the shore neutral, and vice versa - normally via a neon so if 240v Live appears on the Neutral conductor to Ground / Earth at the boat end the lamp illuminates indicating a connection reversal either in the shore power line or shore connection point.)
To clarify there is no 'Positive' inside an AC connection box.
N within an AC connection box does not ever mean negative.
Except black and red were standard colours for fixed AC wiring up until the standards changed in 2006, and the boat was made in 1999.
Indeed - but Red was then Live - Red = Danger. Your installation has the lives apparently on the black cables. Clearly the blue wires are not on the Neutral connections on the sub-breakers.
Ok., live and neutral, not positive / negative.
My brain auto flips to pos / neg with red and black. Probably a good thing the standards were changed !
Agreed, which is why I posted this in the first place... more as a WTF has been done here, but I'm sorry that didn't come across like that in the original post
thats actually quite a special board , hardly anyone uses double pole MCB's
But they should, far safer, in the common case of line & neutral reversed, it isolates both conductors.
I helps with a common boat fault, a defective water heater element that trips the RCD, turn it off on a single pole MCB, the neutral is still connected to the common neutral bar & the rcd still trips.
Should be Line and Neutral.
Common parlance for single phase domestic supplies it is 'Live' and 'Neutral'.
Line refers to one Line phase on a three phase system and whereas it might mean the same thing, Live is the conventional description for the Line (one of three) used on a typical single phase supply derived from any one phase and Neutral. To suggest Live is incorrect is IMHO nonsense unless of course you are a practising electrician.