How thick should my electric wire be?

demonboy

Well-Known Member
Joined
11 Oct 2004
Messages
2,237
Location
Indonesia
www.youtube.com
Is there a formula for working out how thick my electric cable should be, based upon length and ampage draw? I'm installing a water-maker that claims to work at 9amps on 12v and the distance between the unit and the batteries is approx 10m (taking into account bends and bulk-heads etc). I'm trying to use existing cable and holes but worry that it may be too thin.

Thanks!
 
Depends upon what voltage drop is acceptable. Some things, nav lights and distribution boards should be no more than 3%. Other less critical items can deal with as much as 10% voltage drop.

Also depends on ambient temperature where the wires are run and if the wires are run in conduit, bundled together or singularly.

If it were me I would probably use 6mm2 which will give you around a 4% voltage drop at 9A assuming ambient temps of below 35°c with cables not run in conduit.
 
That calculator is really useful, should you use 'there and back' for this calculator too? (i.e for a masthead light, that is say 15m from battery to bulb, would that be 15m or 30?)
 
Remember you also need to de-rate because these equations will be for a single conductor/conductor-pair surrounded by air.
 
I am not sure above the there and back. Some calcs allow for it and others don't. The site I gave I would have to double check any 'instructions' given. /forums/images/graemlins/blush.gif
 
All the advice you've been given is fine but if you have bought a proprietary watermaker I'd email the support department and ask them what they recommend. There should be a wiring diagram showing appropriate fuses, switches or breakers, as well.
 
[ QUOTE ]
I am not sure above the there and back. Some calcs allow for it and others don't. The site I gave I would have to double check any 'instructions' given


[/ QUOTE ] The Engineering Toolbox table requires a there and back figure to be entered for the cable run length.

The EFI calculator is based on a 5% voltage drop so I would not use that one. The basis of the cable run length is not stated either.

THIS ONE is based on a 3% drop (although that can be altered to 4% or 5%) It does not require the cable length to be doubled up to give a "there and back" figure
 