Electric advice

G

Guest

Guest
I am fitting Adverc+blocking diode which requires 16mm cable, as per instruction sheet. Every time I try to buy some its all listed as 'mm square' or 'amps load' can someone clarify please
 

andyball

New member
Joined
1 Jun 2001
Messages
2,043
Visit site
careful with those ratings....

Be aware that if you buy "50 Amp" cable, many respectable suppliers list 7mm2 cable as being suitable for 50Amps..... If adverc say 16mm2, buy 16mm2, nothing smaller, and be sure to use decent terminals/crimp tool, or pay someone to crimp the terminals on the cable for you.

Most suppliers list 16mm2 as capable of carrying around 110Amps, for "average"? use.
 
Top