Well-Known Member
The sensor in a seperate stand pipe looks to be a neat solution to me.
We had a similar arrangement on some scrubbers at work, well it was a totally different sensor but that doesn't alter my point.
When the pump was running there was a pressure drop in the stand pipe so to get a propper reading we had to stop the pump, not a problem for you since your pump will normally be stopped not running as ours was.
The thing is, when the scrubber tank was low level, the liquid in the stand pipe dropped enough so that air was sucked into the pump along with some liquid which is precisely what you are trying to avoid.
A way round this is to fit a valve in the level tube to stop the pump sucking air in when the tank level is getting low. You just open the valve, let the liquid level settle and then take a reading, shut the valve again till next time.