We have a VSR between the engine and domestic batteries (and another from domestic to bow thruster).. An issue we has the other day was that something had been left on and it flattened the domestic battery to 8.2v.. The VSR has a lockout at 9.5v (which I just discovered) so even with the engine running and charging at 14.2v the relay never closed and so the battery would not charge.. This meant the plotter would not run, nor would anything else on the domestic side..
The solution was to use a piece of wire and bridge the engine and domestic positive terminals.. Doing this for about 30sec caused the relay to see a high enough voltage and so close and from there on the battery charged up and all was good..
So going forward I am planing on adding a method of bridging the positives without having to empty the storage to gain access to the back of the battery isolator switches in case this ever happens again..
Just thought I would post for anyone else who uses VSR's to charge multiple battery banks..