Maine Sail
Well-Known Member
Different ways
There are many ways to skin the cat. My monitor is set to more accurately represent a full charge on my system. My charge % is set to 1% as that is more closely representative of the acceptance my bank has at near full (98-100%). 2% acceptance still takes a few hours of charging before my bank is accepting closer to 1% acceptance.
Setting up the monitor parameters depends upon your "system". I think there is a LOT of misunderstanding out there when it comes to batteries, charging, acceptance, CEF, Peukert and monitors in general. For me I don't accept the 2% built in "charged" parameter as 100% because it is not on my bank.
Even though I have tweaked my monitor to best work with my system I still manually re-calibrate at least once per week.
One thing that also happens is that most chargers won't "float" with a load applied. My chargers float, on my bank at full charge, is under 2 amps. Any load of more than 2 amps, and sometimes even less, takes me right out of float.
Of course this all depends on your charger and the "load" but a fridge kicking on can quickly move your charger out of float voltage and put it back into delivering an absorption voltage. Most meters properly set up will not re-set until %/time/volts are achieved for longer than five minutes. With loads running, while charging, you may never re-set because multiple parameters are required..
In my case, with my charging system, it is 1%/13.4V/5 minutes. On alternator it will not re-set as I am unwilling to run my engine for 8+ hours to achieve this so get it back to about 85-90% SOC then I manually re-set when the solar panel has had time to sufficiently top off the bank when it is showing about 1% acceptance.
As sailors we need to get every amp hour out of our cruising banks. Setting up your monitor to leave precious ah's on the table can lead to deeper discharges which can ultimately shorten battery life. 2% acceptance on my bank is not fully charged.
This is an example of a 200 ah bank when used cruising on the hook with only an alternator.
SOC = state of charge
DOD = depth of discharge
Total Bank Capacity = 200 ah
DOD to 50% SOC = 100 ah
Max alt recharge = 80%
Usable Ah's = 60Ah
200 Ah @80 SOC = 160 Ah's
160 usable @80% SOC to a 50% DOD (100 Ah's) leaves 60 usable Ah's before you hit a 50% DOD..
Total usable Ah's, when cruising and charging off the alt, from a 200 Ah bank = 60 Amp Hours !!!
To me every counted Ah counts and leaving mine at 2% acceptance was not something I was happy with..
In this scenario, which is actually quite accurate, you only really have 30% of the capacity of your entire bank to use when out cruising and only charging off the alternator.
Sadly in a situation like this a monitor will only count amps because it would take hours and hours and hours to ever hit float and totally re-charge the bank for an automatic re-set. Furthermore if your alt is single stage regulated you'll need to change the volt parameters too as it will never hit 13.4v, 13.6v, 13.7v etc. as the regulator does not have a "float" setting..
In short slapping in battery monitor and expecting it to "work accurately" is not really a plan that will result in the performance you'd like to see. There are LOTS of variables to more accurate battery monitor performance and all of them need to be considered..
There are many ways to skin the cat. My monitor is set to more accurately represent a full charge on my system. My charge % is set to 1% as that is more closely representative of the acceptance my bank has at near full (98-100%). 2% acceptance still takes a few hours of charging before my bank is accepting closer to 1% acceptance.
Setting up the monitor parameters depends upon your "system". I think there is a LOT of misunderstanding out there when it comes to batteries, charging, acceptance, CEF, Peukert and monitors in general. For me I don't accept the 2% built in "charged" parameter as 100% because it is not on my bank.
Even though I have tweaked my monitor to best work with my system I still manually re-calibrate at least once per week.
One thing that also happens is that most chargers won't "float" with a load applied. My chargers float, on my bank at full charge, is under 2 amps. Any load of more than 2 amps, and sometimes even less, takes me right out of float.
Of course this all depends on your charger and the "load" but a fridge kicking on can quickly move your charger out of float voltage and put it back into delivering an absorption voltage. Most meters properly set up will not re-set until %/time/volts are achieved for longer than five minutes. With loads running, while charging, you may never re-set because multiple parameters are required..
In my case, with my charging system, it is 1%/13.4V/5 minutes. On alternator it will not re-set as I am unwilling to run my engine for 8+ hours to achieve this so get it back to about 85-90% SOC then I manually re-set when the solar panel has had time to sufficiently top off the bank when it is showing about 1% acceptance.
As sailors we need to get every amp hour out of our cruising banks. Setting up your monitor to leave precious ah's on the table can lead to deeper discharges which can ultimately shorten battery life. 2% acceptance on my bank is not fully charged.
This is an example of a 200 ah bank when used cruising on the hook with only an alternator.
SOC = state of charge
DOD = depth of discharge
Total Bank Capacity = 200 ah
DOD to 50% SOC = 100 ah
Max alt recharge = 80%
Usable Ah's = 60Ah
200 Ah @80 SOC = 160 Ah's
160 usable @80% SOC to a 50% DOD (100 Ah's) leaves 60 usable Ah's before you hit a 50% DOD..
Total usable Ah's, when cruising and charging off the alt, from a 200 Ah bank = 60 Amp Hours !!!
To me every counted Ah counts and leaving mine at 2% acceptance was not something I was happy with..
In this scenario, which is actually quite accurate, you only really have 30% of the capacity of your entire bank to use when out cruising and only charging off the alternator.
Sadly in a situation like this a monitor will only count amps because it would take hours and hours and hours to ever hit float and totally re-charge the bank for an automatic re-set. Furthermore if your alt is single stage regulated you'll need to change the volt parameters too as it will never hit 13.4v, 13.6v, 13.7v etc. as the regulator does not have a "float" setting..
In short slapping in battery monitor and expecting it to "work accurately" is not really a plan that will result in the performance you'd like to see. There are LOTS of variables to more accurate battery monitor performance and all of them need to be considered..