Just to add a little more to the mix...
I have a bep dcm600 battery meter and great bit of kit it is too, gets used a lot. But I from experience I don´t trust the accuracy of state of charge from the amps in/out displayed. Also from the manual...
Charge efficiency
Charging Efficiency is set at 85% (factory default) ie the battery will only accept 85% of the charge current.
This is a difficult parameter to set as after 75% recharge the efficiency will fall off to 0% at full charge. The
overall efficiency will change with temperature, battery condition, charging current/voltage and discharge level.
Trial and error with general usage is the only way to find this efficiency.
And about Peukerts exponent...
NB: 0.01 change to Peukerts can make a reasonable change to calculated discharge. Alter in small steps.
For example, 100 Amps for 1 hour = 100Amp hours. Using Peukert’s exponent of 1.25, An x T, 1001.25*1=316
Amp hours. A 25% exponent change makes 316% change.
Calculating exponent “n” from discharge cycles is the only way to achieve an accurate discharge exponent.
This meter comes with a factory set exponent of 1.25, which is a “rough average for deep cycle flooded lead
acid.
If you do not wish to calculate “n” use the tables below to select a typical “n” for your battery type.
If after some time or use (6-12months) the accuracy seems to be degrading (possibly due to battery condition,
temperature, age – charging regime) it will be time to recalculate “n”.
I can´t see how you can rely on the accuracy of amps in/out to determin when a bank is charged. I have the "reset to 100%" set to less than 5a (200Ah bank) and 13.7v (from memory) for more than 5 minutes. Then if the fridge goes on the vlotage drops to below 13.7v and the unit won´t reset. Seems to work well.
I have a bep dcm600 battery meter and great bit of kit it is too, gets used a lot. But I from experience I don´t trust the accuracy of state of charge from the amps in/out displayed. Also from the manual...
Charge efficiency
Charging Efficiency is set at 85% (factory default) ie the battery will only accept 85% of the charge current.
This is a difficult parameter to set as after 75% recharge the efficiency will fall off to 0% at full charge. The
overall efficiency will change with temperature, battery condition, charging current/voltage and discharge level.
Trial and error with general usage is the only way to find this efficiency.
And about Peukerts exponent...
NB: 0.01 change to Peukerts can make a reasonable change to calculated discharge. Alter in small steps.
For example, 100 Amps for 1 hour = 100Amp hours. Using Peukert’s exponent of 1.25, An x T, 1001.25*1=316
Amp hours. A 25% exponent change makes 316% change.
Calculating exponent “n” from discharge cycles is the only way to achieve an accurate discharge exponent.
This meter comes with a factory set exponent of 1.25, which is a “rough average for deep cycle flooded lead
acid.
If you do not wish to calculate “n” use the tables below to select a typical “n” for your battery type.
If after some time or use (6-12months) the accuracy seems to be degrading (possibly due to battery condition,
temperature, age – charging regime) it will be time to recalculate “n”.
I can´t see how you can rely on the accuracy of amps in/out to determin when a bank is charged. I have the "reset to 100%" set to less than 5a (200Ah bank) and 13.7v (from memory) for more than 5 minutes. Then if the fridge goes on the vlotage drops to below 13.7v and the unit won´t reset. Seems to work well.