Maybe not quite right (if that's the new saying?)
BS 7671, Regulation 701.512.3 permits 230v socket outlets to be installed in a room containing a bath or shower, providing they are installed 3m horizontally from the boundary of zone 1.
*Zone 1 is limited by the vertical surface circumscribing the bath tub or shower basin and is extended for showers without a basin for a fixed water outlet to a distance of 1.20 m from the centre point of the water outlet.
Not quite sure how I could have said it differently but do correct me
Ref Zone 2.... it's 2.25m above finished floor level.
BS 7671, Regulation 701.512.3 permits 230v socket outlets to be installed in a room containing a bath or shower, providing they are installed 3m horizontally from the boundary of zone 1.
*Zone 1 is limited by the vertical surface circumscribing the bath tub or shower basin and is extended for showers without a basin for a fixed water outlet to a distance of 1.20 m from the centre point of the water outlet.
Not quite sure how I could have said it differently but do correct me
Ref Zone 2.... it's 2.25m above finished floor level.
Not quite right. You are getting confused with "zone 2" which extends to 3m above a bath or shower but only 0.6 m horizontally either side
More detail on many websites eg https://tp24.com/wp-content/uploads/2014/06/Bathroom-IP-Zones.pdf
PVB's socket above the washbasin should be fine provided it is 0.6m above the basin