It sounds like you have a shunt that everything runs through - which means you can trust the monitor to tell you accurately the net flow of current. I'm sure you know this - the useable capacity of your batteries is about 50% of the nominal, so your 110Ah has 55 useable Ah in it. If your 2 fridges are constantly drawing 8A each then your batt monitor will read 16A and your 110Ah battery will be drained in 3.4 hours (55/16 = 3.4).
Did you say that you have 2 110Ah batteries, and they're drained in 6h? - That sounds about right, based on the above calculations assuming no input. If you know each fridge draws 8A, then your solar is giving you 16A-whatever your battery monitor reads.
So here's the equation for what you can reasonably expect:
Number of hours to flatten batteries = ([Nominal capacity]/2)/[shunt current drain reading]
What does your shunt monitor read?
Is your nominal capacity 220Ah?
Did you say that you have 2 110Ah batteries, and they're drained in 6h? - That sounds about right, based on the above calculations assuming no input. If you know each fridge draws 8A, then your solar is giving you 16A-whatever your battery monitor reads.
So here's the equation for what you can reasonably expect:
Number of hours to flatten batteries = ([Nominal capacity]/2)/[shunt current drain reading]
What does your shunt monitor read?
Is your nominal capacity 220Ah?