Thanks, well yes this is what I had in mind.Connecting the three 100W panels in series and then connecting this to the 455W panel in parallel is the best of the bad options.
The 3 are already in series, so they can stay in series and then I just have to add a Y connector to parallel them to the other larger panel right? Would I require two Y connectors, one for positive and one for negative of just the one for the positive line?
The maximum current of the input wires in this configuration is around 15A, so there is no issue with the current capacity of the existing 10AWG wiring, although voltage drop may further decrease the system’s efficiency depending on the length installed. However, the output wires from the solar controller may need to be thicker than 10AWG with new configuration.
Ok, good. You say from the solar controller, but from the solar controller to where? You mean between the solar controller and the Y connector junction where all the panels meet?
The total there would be 20A or so yes? 15A (around that, don't have the stats handy for the panel) for the large panel, then the 5.2 for the series panels? Is that the right calculation?
Also would I be wanting to add additional fuses anywhere? The existing 3 in series are not fused currently as I was advised on setup is wasn't necessary as they have fuses included or some other built in protection mechanism.