Worrying LPG readings in my gas locker

geegrrl

Member
Joined
11 Aug 2013
Messages
32
Location
London
electricsirena.co.uk
My ALDE gas detector bubbler was showing bubbles. I was unable to find the leak so bought this handheld gas detector which is said to be very accurate. http://www.amazon.co.uk/Honeywell-Sense-Hand-Held-Detector/dp/B008ASXV8W

The detector gave a medium signal in the grill area of the oven. So I shut off and unhooked the lpg bottle. Then I tested the area in the locker where the lpg bottles reside and got intermittant high readings. There are 2x 15kg butane bottles in there. Neither are hooked up or turned on. The readings are intermittent and I can only assume some gas leaked out from turning the bottles on and off a few times for testing.

I'm guessing the grill is leaking . But why am I getting readings in the locker once the gas bottles are closed and unhooked?

Should I be worried? The BSS inspecter passed my gas setup a few months ago.
 
My ALDE gas detector bubbler was showing bubbles. I was unable to find the leak so bought this handheld gas detector which is said to be very accurate. http://www.amazon.co.uk/Honeywell-Sense-Hand-Held-Detector/dp/B008ASXV8W

The detector gave a medium signal in the grill area of the oven. So I shut off and unhooked the lpg bottle. Then I tested the area in the locker where the lpg bottles reside and got intermittant high readings. There are 2x 15kg butane bottles in there. Neither are hooked up or turned on. The readings are intermittent and I can only assume some gas leaked out from turning the bottles on and off a few times for testing.

I'm guessing the grill is leaking . But why am I getting readings in the locker once the gas bottles are closed and unhooked?

Should I be worried? The BSS inspecter passed my gas setup a few months ago.

I dont know about "very accurate" but it is certainly sensitive !

The low alarm comes on at 500 ppm and the high level alarm at 2000ppm. Well below the LEL of butane which ITYWF is 1.6%.


If your Alde shows bubbles you should be concerned about that, Use your EZ Sense to help locate the leak and pinpoint it if necessary with leak detecting spray.
 
I dont know about "very accurate" but it is certainly sensitive !

The low alarm comes on at 500 ppm and the high level alarm at 2000ppm. Well below the LEL of butane which ITYWF is 1.6%.


If your Alde shows bubbles you should be concerned about that, Use your EZ Sense to help locate the leak and pinpoint it if necessary with leak detecting spray.

Good info Vic but for the uninitiated LEL stands for Lower Explosive Limits or the point where gas/air mixture will go bang. :encouragement:

Tom.
 
I was chatting toa retired gas fitter and he told me electronic gas detectors will find leaks leak detection fluid miss. For me as I have little sense of smell it is a godsend. I have found it will detect gas residues in plpes that have been diconected from the gas system for many hours.
 
But why am I getting readings in the locker once the gas bottles are closed and unhooked?

Should I be worried? The BSS inspecter passed my gas setup a few months ago.
You should be worried.

Some gas can leak when you connect or disconnect the regulator.
Remove the bottles from the locker.
went the locker.
measure - when gass free put bottles back in
Measur again before connecting regulator, ok proceed
measur after connecting regulator, ok proceed else went proceed when ok
open regulator and measure any leak in locker should be located now.

Now do similar procedure in the other end.
note that the bubble tester only detect leaks after the tester in the line.
 
No it won't work - as in not create bubles.
To verify that it's working light one burner and do the test routine.
If bubbles OK else refill with more fluid.

I think you will find that the testing correct operation of the Alde must be done with a much lower gas flow than a gas burner or you are likely to blow all the fluid out of the tester into the gas piping. A refrigerator is recommended.
 
Good info Vic but for the uninitiated LEL stands for Lower Explosive Limits or the point where gas/air mixture will go bang. :encouragement:

Tom.

The ppm figures quoted roughly equate to 2% and 12% LEL are calibrated against methane and reading will be different for other hydrocarbons. Typically the alarms are set to 10 and 50% LEL. Methane. Although LEL is the absolute limit gases can be very difficult to ignite at this limit!
 
I think you will find that the testing correct operation of the Alde must be done with a much lower gas flow than a gas burner or you are likely to blow all the fluid out of the tester into the gas piping. A refrigerator is recommended.

I wonder how many boats have a gas fridge?
 
I wonder how many boats have a gas fridge?

very few I would think, more common in caravans at one time perhaps.

I guess it means its difficult to test an Alde on a boat without the risk of blowing the fluid out of the thing. How do people test them or don't they bother?
 
very few I would think, more common in caravans at one time perhaps.

I guess it means its difficult to test an Alde on a boat without the risk of blowing the fluid out of the thing. How do people test them or don't they bother?

Maybe they don't bother. I don't have a bubble tester - so have two less joints to leak!
 
No it won't work - as in not create bubles.
To verify that it's working light one burner and do the test routine.
If bubbles OK else refill with more fluid.

If you do that it will blow all the liquid straight into the gas pipe, you need a very small test leak which is difficult to organise.
 
asleep at the back again? :)

always, luckily the class swat lets me have his notes for revision purposes, he got a first, I got a Desmond.

while you're there, any clues what the fluid is, glycol covers a multitude of sins, and those little sachets cost an arm and a leg.
 
always, luckily the class swat lets me have his notes for revision purposes, he got a first, I got a Desmond.

while you're there, any clues what the fluid is, glycol covers a multitude of sins, and those little sachets cost an arm and a leg.

Usually glycol means ethylene glycol ... as in antifreeze
 
My ALDE gas detector bubbler was showing bubbles..


Was this immediately after you turned the bottle on? Or does the thing consistently record a leak?

I find mine shows a leak at first, and then cheers up. I guess the gas pressure dissipates (I always have the bottle tap off unless using the cooker) and the Alde records the gas filling up the line.
 
Was this immediately after you turned the bottle on? Or does the thing consistently record a leak? I find mine shows a leak at first, and then cheers up. I guess the gas pressure dissipates (I always have the bottle tap off unless using the cooker) and the Alde records the gas filling up the line.

Yes the bubbles from Alde happened immediately after turning gas on. Each time I tried I immediately closed and unlatched the bottle out of fear. So I don't know if the bubbles would subside after a time. But I did leave it on for at least 2 minutes and it did bubble steadily the whole time.

However I did get a reading from the Honeywell EZ sensor when I placed it near the grill in the oven. The calor gas bottle was hooked up and turned on. The grill, oven and all burners were off. The alarm triggered when I pointed the wand at the grill.

I will try the test on the gas bottle locker as suggested by knuterikt.

I do not have a gas fridge so am unable to properly perform the Alde test.
 
Last edited: