The cooker cable is rated at 60 amps continuose, and if my voltmeter is correct the volt drop is so small that I could not measure it at the control panel, length of run about 18 feet.
What current was flowing when you measured the voltage? Of course you would not be able to detect a voltage drop if all you were doing was measuring the static voltage.
No way with Cooker wire could you possibly get no voltage drop on 100 amps flow. You cannot defy physics. The recommended size at 50sq mm is very considerably larger than cooker wire. Go back and check it when the brute is running.