Well-Known Member
If the load is not purely resistive, then watts in not an accurate measure. VA (volt amperes) is a better measure.
Despite a physics degree (some years ago) this is new to me.
Can you explain the difference please.
If the load is not purely resistive, then watts in not an accurate measure. VA (volt amperes) is a better measure.
Despite a physics degree (some years ago) this is new to me.
Can you explain the difference please.
In AC, the current and voltage can be out of phase to a greater or lesser degree.
A pure resistive load will have them in phase, a highly reactive e.g. inductive load will have them moving towards 90degrees out of phase.
A current 90 degrees out of phase transfers no power to the load, but still heats up the wiring etc in the generator. Hence the total current must be limited to what the generator can handle, not just the useful, in-phase current. Hence generators are often rated in kVA not kW.
In AC, the current and voltage can be out of phase to a greater or lesser degree.
A pure resistive load will have them in phase, a highly reactive e.g. inductive load will have them moving towards 90degrees out of phase.
A current 90 degrees out of phase transfers no power to the load, but still heats up the wiring etc in the generator. Hence the total current must be limited to what the generator can handle, not just the useful, in-phase current. Hence generators are often rated in kVA not kW.
Thanks for the excplanations - I understand this so far but how is VA measured.
For AC and a resistive load, I seem to remember that watts is on an RMS basis - effectively the area under a sine wave graph. But if V and A are out of sinc, I assume to measure power theoretically you multiplying them at each point of the cycle and average out the product. How do you actually do this in practice and is the answer watts or VA?
Sorry for fred drift - perhaps I should ask Prof Hawkins -he is on the radio at the moment
Thanks for the excplanations - I understand this so far but how is VA measured.
For AC and a resistive load, I seem to remember that watts is on an RMS basis - effectively the area under a sine wave graph. But if V and A are out of sinc, I assume to measure power theoretically you multiplying them at each point of the cycle and average out the product. How do you actually do this in practice and is the answer watts or VA?
Sorry for fred drift - perhaps I should ask Prof Hawkins -he is on the radio at the moment
I pose this question as I am again without power-just isolate my supply and plug in the 800watt generator and I am back in business.
However the 1500 watt hoover will not work(oh what joy to me but annoyance to my wife) because of course its 1500 watts-but then again my big freezer should not work as it needs about 1000 watts to start up.
My big freezer does work all be it with a total power drop when it starts so what about the 1500 watt hoover-well I know its slow start and possibly brushless and yes it works!
I am sure we all are attracted to both power tools and domestic appliances which tend to be priced according to wattage.
So whats going on-my Hoover does note that its also 200 air watts which sounds like its true wattage so what is the 1500 watts?
Thanks for the excplanations - I understand this so far but how is VA measured.
For AC and a resistive load, I seem to remember that watts is on an RMS basis - effectively the area under a sine wave graph. But if V and A are out of sinc, I assume to measure power theoretically you multiplying them at each point of the cycle and average out the product. How do you actually do this in practice and is the answer watts or VA?
Sorry for fred drift - perhaps I should ask Prof Hawkins -he is on the radio at the moment
So, go on then, who's going to pipe up about Hole and Electron Flow, Co-valent bonding and Crystal Lattice structures????....Arghhhhhhhhhhhh
'snot true. If you are so out of phase so that the peak current is at zero voltage due to the delay imposed by the inductive load, then the integral of AV is going to be clearly less than the RMS product would have you think. You are chucking energy into the opposition of the inductive load which is stopping the current rising in synch with the voltage.Its the product of the rms values of current and voltage, therefore any phase shifts are irrelevant.