William_H
Well-Known Member
Back to the original question. It is not surprising that the VSR is acting strangely with solar charge. The VSR senses when one battery voltage rises to appear to be being charged and connects the second battery to the first battery in parallel. Now at this point of batteries being paralleled you have one battery fairly well charged being connected to an other battery that is low in charge. A large current flows from the charged to discharged battery to equalise the charges. OP reports 20 amps.
This 20 amps will pull down the first battery in voltage especially if it is old and low in capability.
Now in a normal set up where the VSR operates to connect a domestic battery when the engine is charging this drop in voltage caused by the sudden addition of more charge load can be carried by the alternator. (high current capability)
The VSR is usually designed to have a hysteresis where the turn on (paralleling) voltage is much higher than the turn off voltage. So typically 13.0 volts for turn on so detecting engine charging. 12.5 volts for detecting engine stopped charging. The on might be a little higher but should not be so high as to require engine battery to acheive a high voltage before charging the second battery. The off can not be too low or a well charged engine battery might keep it on even with engine stopped.
OK so I imagine the solar charging is not very high current. So it slowly brings the first battery up to on voltage where the relay operates and connects the second battery, however the seconfd battery is so discharged (low in voltage) that the huge rush of equalising current discharges (pulls down the voltage) of the first such that the VSR senses low voltage and opens. So first slowly starts to recharge.
I think OP would be better off with a solar regulator designed for 2 isolated battery banks. (simultaneously) However to swap the primary solar charging to the most depleted battery might solve the problem. But to put it bluntly VSR is not best for solar recharge paralleling. Adjustment of the on and off voltages if adjustable might solve the problem. In any case if the VSR does cycle off and on the solar power is not being wasted and eventually the second battery might rise in voltage enough that in rush current diminishes and it all stops cycling.
Regarding previous argument over battery size and charging efficency (speed). Clearly it is the size of the battery that matters. So 2 small in parallel is the same as one big ie same total AH rating. While the bigger battery (or multiple small ones) will not be discharged so deeply after a given amount of discharge so will not accept recharge so much as if it were deeply discharged, the larger battery will continue to accept more charge even though the voltatge rises with charge. So getting more total AH of recharge witha bigger battery on a limited engine run charge time. good luck olewill
This 20 amps will pull down the first battery in voltage especially if it is old and low in capability.
Now in a normal set up where the VSR operates to connect a domestic battery when the engine is charging this drop in voltage caused by the sudden addition of more charge load can be carried by the alternator. (high current capability)
The VSR is usually designed to have a hysteresis where the turn on (paralleling) voltage is much higher than the turn off voltage. So typically 13.0 volts for turn on so detecting engine charging. 12.5 volts for detecting engine stopped charging. The on might be a little higher but should not be so high as to require engine battery to acheive a high voltage before charging the second battery. The off can not be too low or a well charged engine battery might keep it on even with engine stopped.
OK so I imagine the solar charging is not very high current. So it slowly brings the first battery up to on voltage where the relay operates and connects the second battery, however the seconfd battery is so discharged (low in voltage) that the huge rush of equalising current discharges (pulls down the voltage) of the first such that the VSR senses low voltage and opens. So first slowly starts to recharge.
I think OP would be better off with a solar regulator designed for 2 isolated battery banks. (simultaneously) However to swap the primary solar charging to the most depleted battery might solve the problem. But to put it bluntly VSR is not best for solar recharge paralleling. Adjustment of the on and off voltages if adjustable might solve the problem. In any case if the VSR does cycle off and on the solar power is not being wasted and eventually the second battery might rise in voltage enough that in rush current diminishes and it all stops cycling.
Regarding previous argument over battery size and charging efficency (speed). Clearly it is the size of the battery that matters. So 2 small in parallel is the same as one big ie same total AH rating. While the bigger battery (or multiple small ones) will not be discharged so deeply after a given amount of discharge so will not accept recharge so much as if it were deeply discharged, the larger battery will continue to accept more charge even though the voltatge rises with charge. So getting more total AH of recharge witha bigger battery on a limited engine run charge time. good luck olewill