Ok so I was my webcasts heater gave a low voltage warning and I've recently installed a 12v fridge.
Before startup the voltage in both was 12.65v on batteries only and now shore power. At startup each shot down for a split second and then settled out at:
Fridge: 11.5v
Heater: 10.2
The heater went into shutdown due to low voltage but fridge continued. So as a solution I clearly need to wire decent gauge wire to each directly rather the routing to the big switch panel as it is now.
However I clearly need to switch each one on or off so what's the general solution to this? Have a relay which is switched by the current 12v supply?