The pictures seem to have gone !
hi so your saying take the starter battery and the inverter neg to the bus bar as per first picWe'll it seems you DO have other connection(s) to the domestic bank negative, apart from the shunt.
As we have all said numerous times, the negative side of the domestic battery bank must ONLY be connected to the shunt ..... not to the starter battery negative ..... not to anything else. (as per VicS diagrams).
ALL other connections should be to the other side of the shunt (or to a something connected to the other side of the shunt, such as a busbar or the engine block).
Vic
hi so your saying take the starter battery and the inverter neg to the bus bar as per first pic
if thats the case il try that cheers Mark
................................................................................
(VicS .... pics are there OK for me)
Vic
That's odd all I see are messages that say they have been moved or deleted.
![]()
The pictures seem to have gone !
Is this OK?
They must have been deleted after you viewed them and you are now viewing cached pictures on your computer.
No, same two messages.
I can edit the links and go to the album where they should be. http://s441.photobucket.com/albums/qq139/lockkeeper01/
but they aren't there.
They must have been deleted after you viewed them and you are now viewing cached pictures on your computer.
Or something...?
Agree. Tried to do a screen-grab but failed miserably. Basically the pic showed the two domestic batteries paralleled, with quite a few further connections to the two negative posts.
Vic
No, same two messages.
I can edit the links and go to the album where they should be. http://s441.photobucket.com/albums/qq139/lockkeeper01/
but they aren't there.
They must have been deleted after you viewed them and you are now viewing cached pictures on your computer.
Or something...?
Other shot appears to have a lot of power electronics in a small area, with two heatsinks the wrong way round.
Brian
I now have to go to the hassle of actually removing the positive battery connections each time I leave the boat, else after a week the monitor will show a total loss of charge of 35A.
hi Brian it is a small area i have fitted another fan to work in line with the fan you see on top of the heatsink
. I have reached the conclusion that the zero setting is dependent on the precise battery voltage, suggesting poor internal voltage regulation in the BM-1. Temperature may be a factor, but I'm sure it is predominantly voltage related.
You can get a cheap digital thermometer with a remote sensor, on Ebay for a couple of quid, allow you to keep your eye on the temp. The heatsinks should have the fins vertical, two look horizontal, if you are looking down onto them.
Brian
It's one of the problems with battery monitoring, current counting or trying to read voltages, to many variables, what you get is only a guide.
hi Brian can you send us a link to one of these digital thermometer cheers Mark
True, and I am quite happy working around the limitations as indicated. After all this is relatively cheap mass produced equipment ..... not top-end laboratory stuff.
I think though it would save people a lot of confusion if the manufacturers were a bit more honest and acknowledged the limitations, rather than make bland comments like "the instrument MUST be left connected at all times to ensure accuracy". In the case of the BM-1 specifically this is blatantly untrue.
Vic