why?
[1] Split at socket: the "inner" cable takes twice the load of the "outer"
[2] 10A RCB: why limit the current when you could have 16A?
why?
[1] Split at socket: the "inner" cable takes twice the load of the "outer"
[2] 10A RCB: why limit the current when you could have 16A?
1. Provided the wiring is rated above the breaker, so what?
2. He said milliamps, RCD and RCBO. What have any of those got to do with the rating of the MCB?
A 10mA RCD (rather than 30mA) is a good idea, never seen one that will fit in a CU though.
... you can spur it off another socket or direct from the RCB (see BS7671 Appendix 15 and 433.1, 433.4.1 and 434.4 if in doubt)...
Out of interest, what are Marina individual shorepower loads generally limited to?
Nigelmercier, if you look at the radial circuit in appendix 15 (the second diagram), it states “An unfused spur may be connected to the origin of the circuit in the distribution board.” ...
It won't be a spur off a radial though. He's only got one socket at present, so he'll simply be extending the one outlet radial which is already in place.
See my underlining.
Err... that is a spur off a radial. See above.
A spur off a radial will have three cables in the pattress at which the spur originates...
Simple numeracy I would imagine.Why so?
Simple numeracy I would imagine.
Such simple numeracy ignores the fact that a spur does not involve a third wire, viz:
The wrong way:
[CU] ---- [SOCKET] ---- [SPUR SOCKET]
The right way:
____ /---- [SOCKET]
[CU]{
____ \---- [SOCKET]
Such simple numeracy ignores the fact that a spur does not involve a third wire, viz:
The wrong way:
[CU] ---- [SOCKET] ---- [SPUR SOCKET]
The right way:
____ /---- [SOCKET]
[CU]{
____ \---- [SOCKET]
By that token, the lights in more or less every home in the UK are wired 'the wrong way', since they're radial circuits...
Indeed they are. But the difference is that they are fused at less than 50% of the rating of the conductor. This discussion is about using a 16A MCB to feed a pair of 13A sockets, using flexible cable.
Yes and the maximum total loading on the radial circuit would be 16 amps. ...