That looks like TN-S as you said.
The cut-out (cream unit) is an old type and so probably not the sort usable for TN-C-S. If you had this system there should be a label stating that you are connected to Protective Multiple Earthing (PME).
It has been known for some 'electricians' to do a DIY PME connection (earth to neutral) - this is very dangerous as the supply network requirements for PME are very different. It may be that he was removing something like that.
Check with your supplier if you have any doubts - they should really have upgraded that cut-out by now.