About to get new inverter: cont. power 2500W; peak load 3000W (3s) ; 4000W (0,2s). According to the manual minimal DC fuse (slow blow) is 300A and minimal cable size 95 mm².
1) Should I get 350A or 400A fuse?
2) Would it be okey to combine two 50mm² cables instead of a single 95mm² cable?