Marlec will themselves answer your questions.
And this is what they said:
1) How does the regulator slow the generator?
This is by PWM ( pulse width modulation ). In a nutshell as battery volts rise above a trigger level the regulator issues a pulsed signal to short circuit the Windcharger output. As battery volts continue to rise the pulses get longer until at a maximum battery volts they are united as a full short circuit. At this point the turbine is unable to rotate faster than an "idle" speed.
2) Is it bad for the generator to be left switched off for a couple of weeks? (The manual says not to tie it off for extended periods)
If the regulator is switched off then a full short circuit is applied to the Windcharger and the turbine is stalled and is unable to rotate faster than an "idle" speed. This is a good thing to do as the turbine will dispel water that may otherwise find its way into bearings should the machine be disabled by tying the turbine up.
3) Is the regulator drawing current from the batteries (which are not being otherwise charged) at a significant rate in slowing down the generator.
Yes the regulator draws only a few milliAmps at all times and this is maximised to no more than about 20mA during regulation. However during regulation ( except for a full short circuit ) some charging of the batteries still occurs.
4) Was I being over cautious in switching it off in the light of the forecast (F8/9)?
Mark you did exactly what I would do. The loss of a few battery Amphours is far less than the loss of a Windcharger ! Very wise indeed. This also could have been a case for tying the turbine off just until the conditions passed. If the stall on a Windcharger is overcome by very strong winds then the generator is in danger of burning out.
As Jerrytug suggested they answered the questions quickly and mostly in terms that I could understand. Great after sales support.
Thanks to everybody for your responses as well.
Mark