My 6kVA has been working on and off. Fixed it with a bad cable connection to the battery. Then..it started making large clunking noises coming from the generator not the mitsy engine. Any ideas? Is it worth fixing on an old tatty generator? If I can get the parts that is..thanks JustinHi Dave, I just replied to your PM but for the benefit of others that have this type of generator:
Yes, the capacitor is the one in the box that sits on top of the generator housing.
Assuming you have not tripped the mains isolator/MCB off, that normally sits close to the generator and isolates the 240v supply from the generator, then hopefully the capacitor has just lost its charge.
You are correct, there is no AVR on the 6kVA it is self exciting.
With the generator not running, you just need to flash 12Vdc across the capacitor, it will spark a little, but don't worry about that, no more than one second should do it.
The capacitor is in a closed loop with the rotor/armature winding, when the capacitor is charged, it should remain so, unless for some reason it becomes discharged of course, which it can do if one of its cables gets wet or earths out. Simply put: When you start the generator, the small voltage across the capacitor is sufficient to generate a magnetic field in the armature winding which it is connected to, which it rotates, it induces a field in the stator (main) winding, this is turn induces a larger magnetic field in the armature, and so on until the main winding reaches its maximum voltage output 220-240Vac.
What worries me is, if water has penetrated the winding casing, then you may have shorted-out the main winding which could have burned out. Lets hope that's not the case, but if so, I can tell you how you can remove the stator/main winding without taking the entire generator/motor unit out. Wish I knew that before my one went....!
Anyway, try re-energising the capacitor first, leaving the wires connected to it polarity is not important as its a closed loop, if you're not confident, please have an electrician do it, or at least have someone with you just in case.
Do take care, but it is a very simple thing to do and the 6kVA really is a simple and very reliable generator.
Best of luck.
Hi,
No problem, you can have a copy of my manual with my notes, plus the Mitsy engine manual.
I will send you a link so you can download the file direct.
Let me know once downloaded please.
I've seen various threads re these generators but not a lot of info out there. I have a circa 1995 hfl 6kva built in diesel generator. Sometimes, getting less often, it runs ok. However, most of the time it runs for a few minutes and then does a 'fault' shutdown. It does this even if it is electrically isolated from the boat i.e. all switches off. Bizarrely on occasions if the main engines are running it helps. This may be a red herring but thought it worth the mention. I don't have any further info on the unit and there is some black 'dust' from a rectangular port at the base of the unit if that helps? Anyone have manuals for these generators so I know what to test and what parts need to be changed in a service.
Hi John,
I also havethe 4kva HFL and I am struggling with wiring the control panel in, particularly where the prime button wire goes on the generator. Would you mind if I grab a copy of the manual? Thanks heaps.
Ian
Thanks JohnI will email a link so you can download the HFL manual from our server, please let me know once you have it....