Rocksteadee
Well-Known Member
I have just installed a new Generator on a boat, Fischer Panda P5000i NEO. All good until I used a 3 neon plug in tester. It showed a fault as “No Earth” (or earth greater than 50 ohms)
Checked voltage L - PE 108v and N - PE 121v .
This to me implied a floating to isolated PE. Instead of tied to N
Manual states there is a PE - N bridge (shunt) within the inverter (compntrol box).
Measured resistance with DMM. on inverter and is O/C.
I would expect an impedance shunt to measure as a dc low resistance.
Can’t look inside inverter as there is a warranty seal.
Hastle taking it back to manufacturer.
Manufacturer said I can put a a PE - N link in consumer unit ????
RCD still trips
My field was electronics and 40 years ago so electrically I am running out.
Shore power has PE -N reading of 2.5 v ac. What I would expect as they are tied at substation transformer
Is it a red herring?
Is it safe?
Is it a fault?
Checked voltage L - PE 108v and N - PE 121v .
This to me implied a floating to isolated PE. Instead of tied to N
Manual states there is a PE - N bridge (shunt) within the inverter (compntrol box).
Measured resistance with DMM. on inverter and is O/C.
I would expect an impedance shunt to measure as a dc low resistance.
Can’t look inside inverter as there is a warranty seal.
Hastle taking it back to manufacturer.
Manufacturer said I can put a a PE - N link in consumer unit ????
RCD still trips
My field was electronics and 40 years ago so electrically I am running out.
Shore power has PE -N reading of 2.5 v ac. What I would expect as they are tied at substation transformer
Is it a red herring?
Is it safe?
Is it a fault?
Last edited: