I was more in the business of 10kV and enough amps to dim the lights in the next village.
A lot of stuff not earthed at all!
I was never comfortable there TBH.
But it did put other stuff into perspective.
Inverters sometimes use a capacitor to link the neutral to earth, this can give odd readings and generally you are able to fit a n-e link in the consumer unit as suggested by the supplier, I would get them to confirm this in writing then link the n-e yourself, I have had to do this with old inverters in the past.
If you fit the link in the consumer unit It will be between earth and neutral when switched to shore power... there should not be a local link between earth and neutral. If the shorepower supply "polarity" happened to be reversed the link would then short the shorepower supply live to earth as already explained.
If you fit the link in the consumer unit It will be between earth and neutral when switched to shore power... there should not be a local link between earth and neutral. If the shorepower supply "polarity" happened to be reversed the link would then short the shorepower supply live to earth as already explained.
That'll never happen, the shoreside RCD will trip as soon as the power is turned on. That's why the PE-N connection has to be made at the supply, in the OPs case the genset inverter.
At least it should do, but RCDs are electronic devices and can fail . However if the RCD fails to trip the overcurrent protection device will trip
If the shorepower supply "polarity" happened to be reversed the link would then short the shorepower supply live to earth as already explained.
the shoreside RCD will trip as soon as the power is turned on.
The switch controlling the power from the generator should also control the shore power to the onboard consumer unit. It should be a two pole three position switch switching Live, Neutral from both the generator and the shore power, with the Off position in the middle.If a local PE-N connection is made at the onboard consumer unit it will trip the shore power RCD.
In an installation without an RCD (rather than using your unlikely scenario of the RCD failing to trip), if there was a PE-N connection, that would not cause an MCB to trip, there is no overcurrent event.
There is no possibility of the scenario you described ;
because the PE-N cannot exist after an RCD.
The switch controlling the power from the generator should also control the shore power to the onboard consumer unit. It should be a two pole three position switch switching Live, Neutral from both the generator and the shore power, with the Off position in the middle.
The Earth to neutral connection from the generator neutral can be made on the back of the switch on the generator side, or anywhere along the supply cable back to the generator, but ideally as close to the generator as is feasible, and without any further switch or break point provided.
Such a switch makes it impossible to have both shore and generator connections live to the consumer unit at the same time. Thus the idea of earth connected to neutral in more than one place cannot arise.
Errrrr...?? What do you mean when "the power is turned on"?
Surely you know how to turn the power back on ?
If you were to short neutral to earth downstream of an RCD, it would not trip as soon as the power is turned on, assuming no load. This is because no fault current would exist.
You would find however that once you start to put a load downstream of the RCD, that it would disconnect, once the RCD senses a fault (imbalance between sum total of L and N respectively).
Because you are rattling on a about a situation in which with correct wiring and switching cannot arise.Why are you telling me this ? I'm not the one who suggested a PE-N connection at the consumer unit.
If you were to short neutral to earth downstream of an RCD, it would not trip as soon as the power is turned on, assuming no load. This is because no fault current would exist.
You would find however that once you start to put a load downstream of the RCD, that it would disconnect, once the RCD senses a fault (imbalance between sum total of L and N respectively).