JMcKillop
Well-Known Member
Could some of you knowledable guys give me advice as to where the 230V output socket earth cable should be attached to within the generator. (This is a onboard generator). Does it connect to the battery negative point? 
If your negative is bonded to the engine and other earthing connectors then yes, but you must be careful not to inadvertently create a conducting earth conductor.
This is also where a misunderstanding about what the neutral is and does arises.
In any power source the neutral is connected directly to earth, BUT ONLY AT THE SOURCE This can be at the local HV > LV transformer where the star point of a 3 phase system is usually earthed.
This means that the neutral from the generator should be earthed, BUT IT MUST BE DISCONNECTED COMPLETELY from the rest of the electrical system when the generator is not in use.
The earth system of the boat should also be connected to the metal case of the generator. In turn the generator should be bonded to the engine/s and other bonding circuit components. Now there is some disagreement as to whether or not the Negative should be connected into the bonding circuit, but for most engines it is. This digresses into issues with earth leakage and stray current corrosion. This is not what was asked here.
It is important you must not ever have two neutral earthing points, which is why the switch that isolates the generator should have full pole separation 'Break before Make' for both live and neutral, but not the earth - this remains permanently connected. At the same time it must not be possible to have an external power supply connected to the generator supply unless and only when complex paralleling equipment is provided, and unless you have a super yacht this is highly unlikely to be the case.
For this reason the On (Shore) - Off - On (Genny) switch is essential. Such a switch provides absolute Break before Make safety for two supplies that must never ever meet. Should they meet not only will there be two neutrals to earth, possibly creating a conducting earth system, but also that the phases on the live connection will most likely meet out of phase, however watching the generator rip itself off its bedplate when it attempts to correct the phase difference would be quite interesting.
So to answer your actual question simply connect the 230v socket earth to the generator metal case AND the rest of the bonding / and earthing circuits (note they are not the same thing). When alongside with a generator running, the shore earth connection should be maintained to prevent the boats local ground rising in potential relative to the external true earth. Otherwise someone on the pontoon who is grounded to the shore earth through his feet could get a nasty shock when he tried to board and grabs hold of the metal bonded guardrail.
I have just seen your thread, but its a bit late for the technical / understandable answers. I will respond for you tomorrow when I'm a bit fresher though. I will also PM you some reference manuals you might find of use.Thanks @superheat6k for you technical answer. Mr Google has thown up a lot of technical information that goes way above my head. Let me try and explain my installation. There is a generator/shore power change over switch but not sure if it is break before make. (Will have to check this out). On the 230V distribution board, there is a 30mA RCB and MCBs installed. There is also a Safeshore galvanic isolator fitted onboard. The generator engine is bonded to the battery negative but obviously isolated from the casing by the rubber engine mounts. Currently there is no bonding/earth connection to the casing. Could you please try and explain, "AND the rest of the bonding / and earthing circuits (note they are not the same thing)". Sorry for the lack of terminolgy understanding, must be an age thing :redface-new:.