Gas leak bubble tester positioning

Always check mine monthly or whenever changing the gas bottle, you need to install it where you can see it and test it otherwise why buy it


View attachment 67389

Looking at your photo again, it appears that there are some fundamental errors which wouldn't pass a serious examination.

* The gas bottle locker doesn't have a sealed door
* Having a valve in the pipework before the bubble tester introduces potential leaks which the bubble tester wouldn't detect
* Having so many joints, as well as the valve and the bubble tester, in what looks like a cockpit locker open to the bilge would worry me.
 
..... problem is I can site it in numerous places but none are very accessible. The gas locker is under the lazarette and it would require some considerable life changing contortion to view it !


As long as you are able to press the knob down, a mirror and a torch (like the old gas man) are all you need to spy the thing now and again. So put it near the bottle but don't get fixated about it - it's just not testing the bit between the bottle and the inlet.

It's a very useful device to have in snagging any changes to your system, new flexi pipes etc.
 
Not that this helps the OP that much but I'm refitting my gas this year and opted not to fit a bubble tester.

First reason, It won't fit into the gas locker, well it might, but it's tight enough in there. I wouldn't be able to see it let alone be able to fit the thing (making the joints at the back of the locker). I probably wouldn't use it where it would fit.

Second, it's two more joints and I want minimal joints after the locker as possible.

Thirdly, the boat's survived nearly 50 years without one.

Lastly, I would rather periodicly check the pipework and test each joint with lead detector spray and a handheld gas detector.

When it comes to the boat I like to K.I.S.S
 
Looking at your photo again, it appears that there are some fundamental errors which wouldn't pass a serious examination.

* The gas bottle locker doesn't have a sealed door
* Having a valve in the pipework before the bubble tester introduces potential leaks which the bubble tester wouldn't detect
* Having so many joints, as well as the valve and the bubble tester, in what looks like a cockpit locker open to the bilge would worry me.

The door might have a seal - on the door itself.
Is the locker in the coaming facing outboard? Doesn't need a seal if it is.
How is it open to the bilge? There could be a proper drain.

We need more information.
 
I think you'll find the locker is from Force 4, who describe it as "Ventilation is via a gap under the bottom edge of the door."

Graham is correct the gas locker does have a seal on the door https://www.force4.co.uk/force-4-gas-bottle-locker.html?sqr=gas locker&

The reason the bubble detector is not mounted in the gas locker is simply A) there's no room, B) why would I want to drill more holes in a sealed gas locker.

Any surveyor will tell you Double jubilee clips is 'good practice' on any criticle pipework not to mention they should be fitted opposite each other so the tension on the pipe is equal.

I am afraid when it comes to gas you cannot be safe enough and what you also cannot see is there is a gas detector in the bilges plus the gas locker is vented in the bottom to outside the hull
 
Interesting discussion. Anyone know the details of the Lord Trenchard tragic incident? It was this one IIRC which led to current gas installation practice.

As I recall it, the root cause was that in a dual gas installation, a gas tail was incorrectly fitted when replacing a cylinder, which then became the spare. But when the spare was eventually turned on at the cylinder, the gas then leaked out at the union which had been crossthreaded.

So, from what people have said above, if a bubble tester had been installed, it wouldn't have detected the problem.

That was news to me.
 
Graham is correct the gas locker does have a seal on the door https://www.force4.co.uk/force-4-gas-bottle-locker.html?sqr=gas locker&

The reason the bubble detector is not mounted in the gas locker is simply A) there's no room, B) why would I want to drill more holes in a sealed gas locker.

Any surveyor will tell you Double jubilee clips is 'good practice' on any criticle pipework not to mention they should be fitted opposite each other so the tension on the pipe is equal.

I am afraid when it comes to gas you cannot be safe enough and what you also cannot see is there is a gas detector in the bilges plus the gas locker is vented in the bottom to outside the hull

So the locker door has a seal, but it vents through a gap in the bottom of the door, thereby making it suspect.

Any surveyor should also tell you not to install components between the regulator and a bubble tester!

If you really believe that "when it comes to gas you cannot be safe enough" you'd be changing your installation.
 
My locker vents into the cockpit which vents via the drains.

I assume this is the same setup?

Presumably your cockpit drains are open to the atmosphere. As for Caer Urfa's set-up, I'm not sure. According to Caer Urfa his locker vents into the cockpit which is "normally 'open' unless I have my cover over it when I leave the boat, but as any cover it's not 100% air tight anyway and on my check list switch the gas off when I am not onboard or even when I am not using it." So I'd say it's a bit suspect.
 