t I have no idea what the test button does: does it replicate a fault, or just verifies that trigger will release the switch. I don't need or want to know.
I'll ask an electrician at the yard.
You ask a question and then say you dont need or want to know the answer. !!!! ?????
The RCD trips when you press the button because an imbalance in the current it senses in the live and neutral conductors is created internally in the way captain boo says. It does not create a leakage to earth but certainly does more than just test the mechanical gubbins.
If you were interested in learning anything about this I would offer you this link http://www.select.org.uk/downloads/BEAMA Installation RCD Handbook V2 2010 updated (2).pdf but as you are not please ignore it but please do ensure that your neutral and earth are connected in the supply from the gennerator.
If the earth and neutral are not connected the RCD will not give you the personal ( or fire) safety protection that it should do.