>A GI offers no protection from leakage current from shorepower supplies , or for that matter from defective 12/24 volt installations. Leakage currents from these, and the electrolysis they could cause, is a different matter altogether and potentially more serious because the GI offers no protection.
Again that is wrong which is why metal boat that have a GI don't get stray current corrosion and those that haven't got one have been known to get corrosion from (as I mentioned) shore power, normally caused by a bad earth, and where salt and fresh water mix. We also had a GI on our 12v system.
I wouldn't bother to fit one to a GRP boat but everyone to their own.
No its not wrong.
The whole point of a GI is that it blocks current from very low voltage sources, such as that arising from "dissimilar metals", to prevent galvanic corrosion, in particular rapid loss of zinc from the anodes.On the other hand it allows current from higher voltage sources such as the AC mains power to pass so that safety protection is maintained. Circuit breakers will trip, or fuses will blow in the event of a live to earth fault. RCDs remain fully effective too.
Current from 12/24 volt sources will also be passed as the cutoff point is usually for voltages below about 1.3 volts, although they do vary, so they offer no protection from electrolysis caused by obscure faults on DC systems
I cannot imagine what what you where doing with a GI on the dc system unless you used it as the bond between the DC negative and the shorepower earth as shown in Fig 2 in my diagram that Roger refers to.
GIs are fitted to GRP boats connected for lengthy periods to a shorepower supply to prevent rapid loss of zinc from the anodes due to current from "galvanic sources" being conducted by the shorepower earth....... As I have already said that is why they are sometimes called zinc savers. The only time there is no need to fit one is when the shorepower earth is not bonded to the anodes.