Well-Known Member
Perhaps 20mm was a typo, not like Vics to be so far out.
Ive been over it again and still come up with between 4 AWG and 6 AWG ( 21.2 mm² and 13.3 mm² respectively) but that is for the entire 8m distance (16 metres total wire length) and taking Maplin's Imax of 9,72 amps per panel
Also calculated using some basic physics and a dollop of arithmetic, rather than using tables and online calculators, and arrived at 17.3 mm ² for a 3% volts drop
In either case rounding up comes to 20mm², while rounding down comes to 15mm²