tgalea
Well-Known Member
Hi All,
I decided to go for a battery monitor and have been doing some research but would like your opinion on the following.
I have one starting battery and two 160AH batteries forming the domestic bank. The domestic batteries are paralleled, BUT. For some reason the negative cable coming OUT of the domestic bank is daisy chained to the starter battery negative.
I am only interested in monitoring by domestic bank and like the looks of the NASA BM2 the new 200amp shut version.
Considering my setup, which battery monitor do you recommend.
On a technical note. Since my negatives are chained:
1) Is the shunt connected to the negative output of the domestics before joining the starter negative or should it be at the very end of the chain, i.e, betweent the starter negative and the rest of the negative circuits ?
If the shunt is to go at the very end of the chain, I am correct in assuming that this shunt will need to handle the starting currect of the engine starter motor and therefore 200AMP shunt could be a problem ?
Thanks in advance.
Tyrone
I decided to go for a battery monitor and have been doing some research but would like your opinion on the following.
I have one starting battery and two 160AH batteries forming the domestic bank. The domestic batteries are paralleled, BUT. For some reason the negative cable coming OUT of the domestic bank is daisy chained to the starter battery negative.
I am only interested in monitoring by domestic bank and like the looks of the NASA BM2 the new 200amp shut version.
Considering my setup, which battery monitor do you recommend.
On a technical note. Since my negatives are chained:
1) Is the shunt connected to the negative output of the domestics before joining the starter negative or should it be at the very end of the chain, i.e, betweent the starter negative and the rest of the negative circuits ?
If the shunt is to go at the very end of the chain, I am correct in assuming that this shunt will need to handle the starting currect of the engine starter motor and therefore 200AMP shunt could be a problem ?
Thanks in advance.
Tyrone