W = V x I
Power is proportional to current AND Voltage ( or I squared).
Power is proportional to current AND Voltage ( or I squared).
4??
Three phase uses only three wires.
Is it not three phases plus neutral?
Pete
Depends if it is configured star or delta
3 phase = 3 wires
3 phase plus neutral = 4 wires
Star or delta makes no difference
The centre point will be the neutral if it's "star". Where's the neutral if its "delta"
A step-down transformer will have three balanced windings on the primary side which will receive power from the 3 overhead cables as Vics has shown. It's when it serves an unbalanced load across the 3 phases a 4th cable is required.
I am just trying to figure out how much power I am losing by not upgrading the cable.
I figure that even with very large cables I am going to lose say 5%. If I am only losing 10% with my current cable, then I am not that fussed. However if it is up to 20% then it needs to be added to the list of jobs to do.
for a 12v system with your cable run, air breeze recommend 16mm^2 cable. Cable power losses aside, smaller cables will also reduce the voltage at which the W/G begins to regulate - i.e. prematurely stops charging your batt. bank. Your W/G outputs DC, so 3-phase considerations not relevant.
And that compares closely enough with my suggestion, in post #4, that 15mm² cable would be about right.![]()
I was speaking generally but even then a ground path back to the generating source would need to be employed to take the imbalance, are you talking YD? HV/LV?Not always the case, often when a neutral is not available a transformer connected to two phases is used to supply the unbalanced load