So I installed a 20L marine calorifier in my VW Transporter van.
My van had a second heater in the rear, a paralel circuit with the cab heater.
I removed the rear heater and plumbed in the calorifier in this loop.
I am not satisfied with the performance of the calorifier.
The main problems are:
A. Volume
My target for a hot shower for 2 people was 20-30 liters.
My install is practically flowing 8L/min from the shower head (with a 14L/min pump)
from SureJust website:
* not the manufacture of my calorifier but just as a reference
calculating on this quote....
20L @ 85°C
25L @ 65°C (25% increase)
26L @ 45°C (30% increase)
28L @ 40°C (40% increase)
When I drive more than an hour, so the water should be around 85°C, my results are this:
! thermostat tempering valve set to 65°C, mixer tap full open to HOT
1L @ 46°C
10L @ 45°C
20L @ 28°C
30L @ 23°C
40L @ 20°C
> So why don’t I get 65°C to start with?
> Another concern that I have, if I consume 10L from my 20L calorifier taking a shower, those 10 liters will be replaced by 10 liters COLD water from the holding tank, since it’s a pressurised system - Right?
The hot water will be in the top and the new cold water pushed in the bottom.
But does it mix after all lowering the overall temperature in the calorifier?
> Was I expecting to much of a 20 liter model?
B. Heat Loss
When I drive more than an hour (85°C), park up for the night (lets say 10°C air temp overnight), the next morning the water is just barely warm!
Not even one shower… The manufacture from the calorifier says the temp drops 1°C/hour in 24h, but in reality it’s way more faster.
By now I insulated the pipework as best as I could and will also use two shut-off valves in the coolant loop to prevent heat creeping up vs the engine, but I doubt it will change a lot.
My van has an air heater (usually set to 18°C for the night) and I even routed the ducting just next to the calorifier with this in mind.
There is a definitely some heat radiation going on in the box where I installed the calorifier, even with the pipework insulated now.
> What else can I do to prevent heat loss?
My van had a second heater in the rear, a paralel circuit with the cab heater.
I removed the rear heater and plumbed in the calorifier in this loop.
I am not satisfied with the performance of the calorifier.
The main problems are:
A. Volume
My target for a hot shower for 2 people was 20-30 liters.
My install is practically flowing 8L/min from the shower head (with a 14L/min pump)
from SureJust website:
* not the manufacture of my calorifier but just as a reference
The stored water within the boiler reaches the same temperature as the engine (generally 85°C). If the mixer valve is set at 65°C you will generally increase your available hot water supply by 25%.
calculating on this quote....
20L @ 85°C
25L @ 65°C (25% increase)
26L @ 45°C (30% increase)
28L @ 40°C (40% increase)
When I drive more than an hour, so the water should be around 85°C, my results are this:
! thermostat tempering valve set to 65°C, mixer tap full open to HOT
1L @ 46°C
10L @ 45°C
20L @ 28°C
30L @ 23°C
40L @ 20°C
> So why don’t I get 65°C to start with?
> Another concern that I have, if I consume 10L from my 20L calorifier taking a shower, those 10 liters will be replaced by 10 liters COLD water from the holding tank, since it’s a pressurised system - Right?
The hot water will be in the top and the new cold water pushed in the bottom.
But does it mix after all lowering the overall temperature in the calorifier?
> Was I expecting to much of a 20 liter model?
B. Heat Loss
When I drive more than an hour (85°C), park up for the night (lets say 10°C air temp overnight), the next morning the water is just barely warm!
Not even one shower… The manufacture from the calorifier says the temp drops 1°C/hour in 24h, but in reality it’s way more faster.
By now I insulated the pipework as best as I could and will also use two shut-off valves in the coolant loop to prevent heat creeping up vs the engine, but I doubt it will change a lot.
My van has an air heater (usually set to 18°C for the night) and I even routed the ducting just next to the calorifier with this in mind.
There is a definitely some heat radiation going on in the box where I installed the calorifier, even with the pipework insulated now.
> What else can I do to prevent heat loss?